Thermocouple card
tkhawkin
Jul 2010
South Carolina
I set up a temperture controller, It works fine now I need to test the thermocouples. What I need to know is, the wire from the test meter to thermocouple the same on a K type and a J type. Thanks
I was under the impression that thermocouple wire IS the thermocouple itself; Joining the two creates a small potential.
Correct, but connecting copper wires to the thermocouple wires creates 2 more thermocouples, giving a total of 3 in series. Thermocouples must be connected with thermocouple extension grade wire and associated connectors to eliminate this.
We must use the same metals for the entire run back to the electronics. At the electronics (terminal block) end, we do have the unavoidable problem of 2 more thermocouples. This is called the Cold Junction. A temperature sensor is added. It senses the temperature of the Cold Junction, and subtracts it from the reading. The net is the reading of the thermocouple we want - the Hot Junction.
See this well written paper from Omega.
a thermocouple is two different types of wire connected. so no they are not the same.
testing is simple.
use a short copper wire and the result should be the surrounding temp.
use a thermocouple wireset and twist the end. making an electrical connection.
now connect the two wires and heat the other end up.
CJ reading gets added to the EMF reading/conversion, not subtracted.
Hi All, since it is discussing about the thermocouple, i got some issue on this.
I'm using Delta PLC and DVP04TC module, i just cant read the temperature, everything show K0. Please help.
I used the template, it doesn't work.
Is it possible to wire a J type Thermocouple directly to a Allan Bradley Analog input card, specifically a 1769-IF4 card, and scale the reading to...
2,567
So I finely got everything ready to go with me analog thermocouple cards and no having an issue with actual temperature. Here is the problem at...
26
5,503
I had a question about thermocouples and analog card. I have a 1762-if20f2 and i am useing the outputs to control a vfd and i am trying to use the...
1,949
Hey guys. I'm looking for an inexpensive way to integrate 4 load cells into a project. Right now, the project is using an Arduino with a HX711...
7,183
i have testing controlling temperature using a micrologix 1400 and the Allen bradley 4 channel thermocouple input card. not in the office so do...
5,698