if you have a motor that you put a amp clamp on and it is pulling 28 amps across each phase, and is a three phase motor.
is the total current draw equal to 3*28, or is it 28 amps.
Does anyone know of a good web page with calculators, formulas, etc. to help with questions such as this.
thanks
This is basic electrical theory. While it is possible, there is no practical reason to combine the individual 3-phase line (or phase) currents to come up with a single number.
Originally posted by wescEngineer:
Current as labeled on the motor should be around 28 amps but power is (3)^1/3 * V * I * Eff * Pf (units in watts).
I'm pretty sure the equation should be:
31/2 * V * I * Eff * PF
as opposed to
31/3 * V * I * Eff * PF
as listed above.
Keith
as opposed to
as listed above.
Keith
It is, another way to display is the square root of 3 (1.73)*V*I*EFF*PF
That would be the mechanical energy output of the motor, accounting for energy inefficiencies.
The energy consumption of the motor is
31/2 * V * I * PF
First lets note that the square root of 3, which is used with 3 phase calculations, is 1.73
To obtain watts it is 1.73*V*I*PF, to obtain KW divide that by 1000.
To get HP (output) you use 1.73*V*I*EFF*PF divided by 746
As mentioned the formuals are shown here: http://www.patchn.com/motorformula.htm
V and E are both used to express voltage.
Hello, I have a application where I have a threepase transformer that gives 22V AC 50 Hz. I use A Three Phase Rectifier Bridge to make DC...
1,932
I'm not having luck finding a definitive answer to whether I should use Time Delay or Fast Blow fusing for 480V, three phase, 36kW heaters. I've...
2,701
Hey, this might be a simple question, but I don't think I ever ran into it before. We all know that on 3ph, any two leads can be swapped to...
26
7,049
Hi everyone, I am part of a senior design group that is building a dynonameter to test shocks. We are ordering parts tomorrow morning and so I...
17
10,128
Hello everyone I ve bought three inverters dc to ac. The input is 24V dc and output 230V ac. Each of them 3kVA. I want to link them together to...
1,854