Tricky simple controller relay circuit

how about this circuit?

It's good but it's not really needed in industrial PLCs.

The circuit will work the same but what you have done is put a flyback diode over the relay coil. It will dissipate the current surge that the coil produces when you turn off the relay. So it protects the digital output on the PLC.

A flyback diode is standard practice in electronic design but not in industrial PLCs so I assume that the outputs of a PLC can handle things like this.
 
A flyback diode is standard practice in electronic design but not in industrial PLCs so I assume that the outputs of a PLC can handle things like this.

Adding surge suppression IS standard practice with PLC's.
I have seen many problems caused by this exact issue; of people assuming that suppression is not needed.
Always suppress every coil.
 
wire the relay with a second coil wire off the output ( poor man's latching )

Use the plc to break the neutral line. that will drop the coil when program is complete.

Or I'm complete off the mark. In which case, see comments below
 
Adding surge suppression IS standard practice with PLC's.
I have seen many problems caused by this exact issue; of people assuming that suppression is not needed.
Always suppress every coil.

Let's just say that my experience is not the same as yours.

Since I'm curious by nature I just disassembled an old Siemens PLC (S7-200). I see that there are diodes on every single output - which is what I suspected.
So there is really no need to add additional suppression diodes for regular relays.
 

Similar Topics

Good Eve Gentlemen, We had this cold room which was converted to hot room before I joined this work. Everthing was fine until a month ago, they...
Replies
9
Views
2,116
Hi Here's a question I'm about to ask Omron.. as soon as I can figure out who to ask.. It's complicated asking support.. their web email form...
Replies
2
Views
3,117
Hi all, I am just out of school and working in my first engineering position doing mostly PLC (SLC500) work at a small company. I have been...
Replies
11
Views
3,582
We have faced a tricky problem . The panel view Plus 1000 is not going online..The network guy "Ping" from system and shows that the node is ok...
Replies
4
Views
2,233
Hi guys, Simple question, but I cannot find simple answer to it: How to read the instance DB symbolic name from within FB? If this is not clear...
Replies
7
Views
2,555
Back
Top Bottom