Triggering recurrent action in CCW
MikeBriggs
Sep 2022
Dover, NH
33
In Connected Components Workbench, using ladder logic, is there a relatively simple way to trigger something to happen repeatedly at a regular interval? In my case, I want to send some Modbus messages (reads) every 2 seconds. The CCW timers I'm familiar with all revolve around delaying an action from happening after some event (something becoming true or false) for some amount of time - but not for having it happen repeatedly every X seconds. I might be able to figure out some roundabout way of doing it with a pulse timer....
Thanks!
Even with a standard Delay on timer just use the not output on the input of the timer this will give you a pulse for one scan at the time interval you choose or if you need it on for longer seal a contact in from the timer then clear it when you have finished what you want to do.
AND NOT T4:0/DN [T4:0 2S]
T4:0/DN
------| |--------------On for one scan every 2 seconds
Do Micro8xx PLCs have a Real-Time Clock (typically a data structure or array of integers year, month of year, day of month, hour of day, minute of hour, second of minute)? Or maybe a seconds since the Epoch system DINT?
Because the low bit of the seconds integer will have a rising edge every 2s, and could trigger a Modbus message FB, although they probably should not do so unless the previous message execution has completed (success or error).
System Variable __SYSVA_CYCLEDATE is a timestamp, data type TIME, that gets updated at the beginning of each scan cycle.
It appears (cf. here) to be a running UDINT count of ms, probably since the Micro8xx was powered on and rolling over every three and a half fortnights or so.
Assuming that is true, __SYSVA_CYCLEDATE's bit 10 (value 1024) has a rising edge every 2048ms, accurate to a few ms. Is that close enough?
There is also __SYSVA_CYCLECNT, which counts scan cycles, so if the 2s target period is a round number, then that cycle count could also be used once you calibrate the scan time of your program, e.g. if the mean scan time is around 4ms, then bit 8 would have a rising edge every 2s or so.
Whoopsie! I just remembered:
If this is Modbus TCP, then the MODBUS2LOCPARA structure already has timed repeating capability built in; cf. parameter TriggerType here.
Of course, being CCW, whether it actually works is whole 'nuther kettle of fish.
T4:0/DN
This video starting here is an example of what @parky is suggesting, which is the canonical way to implement a repeating timer.
Contrary to what that video says, the TON_1.Q bit does become 1 for 1 scan, starting at the completion of the TON instruction.
Hi all. I am looking at a valve position which has been scaled for an operator HMI. The valve position is in 0-100% shown to the operator for...
1,137
I have established communication with a sensor via ASCII protocol using the Micro-850 PLC. I have a program which writes to the sensor using an...
1,892
In my lab we are using Controllogix plcs and RS 5000 for programming the PLCS. We have one PLC on a skid, and one PLC at our workbench and we...
1,800
I am measuring level on 36 tanks and wanted to change the color of the tank on the screen as it was being filled or emptied to make it easy to...
2,463
I am trying to add some new transactions to an existing working FactoryTalk transaction manager service (V10.20). One is triggered by a bit (bool)...
2,667