Tutorial: A Level Application
Bernard
Dec 2002
Refer to: SCAN 02-0100
I took the liberty, for my own edification to to identify/individualize the two (2) relay contacts identified as "1000"
Identified them as 1000(A) and 1000(B)
1000(A) latches the relay to complete the circuit when Lo-Level contactor (0000) becomes FALSE.
1000(B) latches the motor (0500) to complete a circuit.
Question: What took place between scan (2) and scan (100) to cause 1000(A) to become true.
The text states that "AFTER" 100 scans the oil rises above the low level sensor and becomes open.
It seems to me that when sensor "0000" is triggered by the oil level that "0000" and 1000(A) would change states simultaneously.
Thanks again for your patience
Bernard
Hi Bernard,
Check the animation link below for a scan-by-scan look.
animation
Review each scan instruction by instruction and you'll soon see that the contact A is evaluated before the coil 1000 and contact B is evaluated after the coil 1000. Therefore, B always follows the coil 1000 on the same scan. 'A' will be a scan 'behind'. Make sense?
Since it's an internal relay its status is updated immediately.
Enjoy,
Bernard, think of each rung as a boolean equation. The program becomes:
1000 = (0000 OR 1000) AND 0001
0500 = 1000
At scan 1, when both 0000 and 0001 are both true, but 1000 is still false, the equation for the first rung evaluates as:
1000 = (True OR False) AND True = True
The value of True for 1000 is used in the solution of the equation for rung 2:
0500 = 1000
0500 = True
Hope this helps.
Question regarding the tutorial: A Level Application Per the text associated with the ILLUSTRATION "Both of our inputs will be NC (normally...
25
15,864
Hi. I am trying to understand some old code for B&R 2005 PLC created in PG2000 software. There are procedures concerning axes but I cannot find...
723
I'm testing the ability to make a custom ActiveX control for PVP7 applications to be able to write data out in an XML format. With my simple...
651
Hi guys, Can you share me any educational links & tutorials for B&R PLC structured text programming? The help section in their automation...
846
Hi all, PLC machine vision is barely talked about anywhere yet it is very important PLC and Industrial automation topic. Like you see vision...
1,059