Twincat 2 Error 3612

ibora

Lifetime Supporting Member
Join Date
Dec 2008
Location
Izmir
Posts
66
Hello everybody,
I'm trying to be online a twincat-2 plc with twincat plc control. But when the program compiling i'm getting an error message with code 3612(Maximum number of POUs exceeded). When i read from Beckhoff site to correct this message Beckhoff is advicing to increase Maximal Number of POUs from controller settings menu.

But when i open project>options i can't see the controller settings menu.
Can someone explain this please? Or how can i correct this error?

Thanks a lot
 
Find your TwinCAT installation path. E.g. C:/TwinCAT/
Find the folder Plc. Open TwinCAT PLC Control.ini file.
Change the line MaxNumOfPOUs=1024 to something like 2048.

I've had projects where 4096 didn't even cut it. Damn OEMs and their one size fits all...
 

Similar Topics

Sorry if this has been asked before, and apologies if this seems like a trivial issue, but I am new to Beckhoff and have been banging my head...
Replies
2
Views
156
Gents, I'm trying get some SEW Movigear motors in control by a Beckhoff PLC which is TwinCAT 3. The SEW motor is connected by EtherCAT and is...
Replies
0
Views
1,314
Gents, I'm pretty new to Twincat 3 and facing at an annoying issue when try to go online with a remote Beckhoff PLC. At out plant we have 10...
Replies
5
Views
4,678
Hello: I have a TwinCAT embedded PLC and for years I was able to access it through the AMS NetID. Recently updated Windows 10 and I was not able...
Replies
6
Views
16,241
Hi! i try to use string as variable name in a forloop my problem is tahat my if insturktion not allow strings as variable name. my declaration...
Replies
7
Views
2,381
Back
Top Bottom