Hi all I did a quick search and couldn't find this specifically.
I always buy 3 wire 24vdc proximity's and wire them (fused terminal) direct to my PLC inputs - It just works.
Our client has specified 2 wire NOT Namur as there is no zoning issues.
Had the Turk sales guy here and he says it can be wired direct as there sensor needs 3mA. My argument is that there is no load.
The input on a PLC is an opto-coupler which needs 4mA to operate taken from a Mitsubishi DI datasheet.
I am sticking to my guns 3 wire straight into Input - I know it works. 2 wire needs an interface relay.
Only referring to 24VDC not AC as this is the control voltage.
Any body got any comments or am I too old school and need to change.