UL508A minimum spacing
Nearbyatom
Jul 2017
USA
38
In the UL book table 10.2 it states that a minimum spacing of 1" needs to be maintained for voltages 251-600V if "through air", and a min spacing of 2" if "over surface" at the same voltages.
What does "through air" and "over surface" mean?
Through air means if you look at the two lugs on a device and look for the smallest air space between them, it must measure 1" or more.
Over surface means the distance is measured as if you were an ant crawling on the surface in as short of a path as possible along a common (non-conductive) surface between terminals, often referred to as "down, over and up". So if for example you have a circuit breaker where the lugs are less than 1" air gap apart, you can add a barrier between them that has a total surface distance from one to the other of 2 inches or more.
Case in point: If you removed those black barriers, the distance between lugs would be less than 1" but with them in place, it is more than 2" across the surfaces.
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
396
Is there anyone that can give me the run-down on differences that are required for control panels sold in European markets, compared to those for...
747
Anybody have a recent experience becoming a UL508A panel shop? If so, how long did it take from initial contact to being able to apply stickers...
1,237
Hello, do 3 PH AC Servo Motors ( 1S Omron) follow the same rules as regular AC servo Motors? can I use Table 50.1 (UL508) to calculate FLC of...
2,041
  • Poll
Luckily, I do not have to worry about this test, but I am creating this poll for atc2222.
36
40,537