Dear,
I need to measure flow on existing pipe 1.6m diameter, and it is not allowed to remove it, so I guess I will go for clamp on ultrasonic flowmeter, however, I only have 4D upstream available instead of the required 10D, do you think the accuracy will vary much in this case?
good day,
Charbel
The real question is not, "will it vary much?", but, "how much will it vary?", because that's always the follow-up question.
And that's an unknown. You don't know because the magnitude of error due to upstream/down pipe geometry flow profile is rarely, if ever, researched and published. The error is acknowledged, but is not quantified.
For other flow technologies, there is some evidence. Siemens published the results of a flow stand test for magmeters with upstream anomalies like elbows in-line or out-of-line where the flow rate error was less than 2% (I was astounded to have finally found actual test results when I read that.) And some years ago, I found four or five references to orifice plate erosion-wear or installed-backwards error, with error rates reading from 10% to 25% low.
But I've never found any published comments on the magnitude of clamp-on error.
Siemens clamp-on flowmeters have a setting that claims to provide some correction for flow profile induced error, but no numbers for what the error reduction is:
The accuracy is not going to be good. It may be good enough depending on the process. More important in most cases is repeatability.
You may not be stuck with clamp-on technologies. There are hot tap systems for insertion type mag meters and insertion ultrasonics that may be applicable. Talk to your supplier.
https://youtu.be/0R_bw0qTf10
Is it good idea to use ultrasonic clamp type of flowmeter for water dosing? I already using the flowmeter pulse output by setting to 10L per...
1,289
Dear, I am wondering if there is an ultrasonic type flowmeter (clamp on) for measuring flow in partially filled pipes. The ones that I was...
3,024
i want to install ultrasonic flow meter at flare lines ( cold and hot)which diameters are 14 and 24 in so i have some questions in this issue...
2,535
dear, i was looking at the ultrasonic flowmeter from E+H, proline prosonic flow 93W, this flowmeter will be used for sewage applications, and...
2,879
Looking at a sensor wired directly to a PLC analog input (DL450) and trying to identify a make and model. Sensor is working, but if I sign a...
3,751