OK, I see it now. I didn't see that the Common on the PLC input was tied to +24.
If you take a jumper and tie a PLC input to the minus side of your 24v power does the input come on then?
@Jerry I do read the input signal in ladder logic when that input port is connected to the -ve terminal of my power supply!
@Bernie Are you pointing something out I've done wrong!?
Well, ok then. Maybe consider bad cable or breakout board. I've seen it.
Just to review then. If your measure near zero VDC between COM and the PLC Input at the ZipLink breakout board (Robot output transistor is OFF) the PLC input (as seen in the program) should be OFF. When you measure approx 24 VDC between the same points (Robot transistor is ON) your PLC input should be seen as ON.
uhmmm! I believe i measure 0V because both plc input and com are at 24V (due to incomplete circuit) and which explains why i read 24V between either points and power supply -ve terminal. For PLC to be on i'd have to read 0V or near 0V between plc input and -ve terminal or 24V between COM of PLC and plc input which i haven't achieved yet unless in the instance when i connected the -ve terminal of my power supply directly to the PLC input with the purpose of verifying my PLC input wasn't fried (turns out its in good condition)
Hi All Whenever i try to change the IP address of a compact logix PLC from RSlinx, this message appears to me "unable to read module's port...
4,469
I am able to write on the drive but unable to read actual position. How can I program the messaging to read?? Pls Help!!
3,225
I have been using dotnet and OPC servers (NI and Kepware) to communicate with Allen Bradley Micrologix 1400 PLC on different environmental...
5,820
Recently we have purchased the Rosemount 752 remote indicator to replace with new one, Capability file for that FF Device is unable to import with...
46
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
299