Could anybody please tell me what algorithm use following S7-SCL code. I understand it is a value as input then making output. But i want to know what formula it has been used .
FUNCTION FC572 : VOID
TITLE = 'Lookup'
// Block Parameters
VAR_INPUT
// Input Parameters
Input : REAL;
X1 : REAL;
Y1 : REAL;
X2 : REAL;
Y2 : REAL;
X3 : REAL;
Y3 : REAL;
X4 : REAL;
Y4 : REAL;
X5 : REAL;
Y5 : REAL;
X6 : REAL;
Y6 : REAL;
X7 : REAL;
Y7 : REAL;
X8 : REAL;
Y8 : REAL;
END_VAR
VAR_OUTPUT
// Output Parameters
Output : REAL;
Lower_Limit : BOOL;
Upper_Limit : BOOL;
END_VAR
VAR_TEMP
END_VAR
// Statement Section
IF Input <= X1 THEN
Output := Y1;
Lower_Limit := TRUE;
Upper_Limit := FALSE;
RETURN;
END_IF;
IF Input <= X2 THEN
Output := Y1 + ((Input - X1) / (X2 - X1) * (Y2 - Y1));
Lower_Limit := FALSE;
RETURN;
END_IF;
IF Input <= X3 THEN
Output := Y2 + ((Input - X2) / (X3 - X2) * (Y3 - Y2));
RETURN;
END_IF;
IF Input <= X4 THEN
Output := Y3 + ((Input - X3) / (X4 - X3) * (Y4 - Y3));
RETURN;
END_IF;
IF Input <= X5 THEN
Output := Y4 + ((Input - X4) / (X5 - X4) * (Y5 - Y4));
RETURN;
END_IF;
IF Input <= X6 THEN
Output := Y5 + ((Input - X5) / (X6 - X5) * (Y6 - Y5));
RETURN;
END_IF;
IF Input <= X7 THEN
Output := Y6 + ((Input - X6) / (X7 - X6) * (Y7 - Y6));
RETURN;
END_IF;
IF Input < X8 THEN
Output := Y7 + ((Input - X7) / (X8 - X7) * (Y8 - Y7));
RETURN;
END_IF;
Output := Y8;
Upper_Limit := TRUE;
END_FUNCTION
Thank you.
The code is rather clunky and would have been better written as a loop but it interpolates between points.
The code scans down the list of Xn values until it finds an Xn entry that is less than Input. By subtracting Xn from Input you are left with a value of X in excess of Xn this is then divided be the value of Xn+1 - Xn and then multiplied by Yn+1 - Yn. This partial result is then summed with Xn to provide a result.
I wrote a similar block that reads in an array of XY points to provide a non-linear interpolation of a linear function. I also wrote a complimentary inverse function that allows you to do a YX lookup on the same data.
Nick
I am using Allen Bradley PLC for Ethernet/IP communication. I send any explicit msg request (Get attribute or Set attribute), I observed packet...
79
Took a new job and the controls schemes are fairly old and I'm used to Allen Bradley and Siemens. I'm looking to replace a pair of Superior...
118
Hello Team, I am desperate for some help with an assessment I have as part of a Level 3 general engineering course. I am in a role that is much...
372
Good day is there somewhere i can see the situation and compatibility regarding different firmware revisions. I have a 2711-K5A5, series H and...
220
Good Evening , I should know more about Solid State Relays . I have a system with 8) 120 vac Vibrators . These Solid State Relays have...
24
2,088