Unreferenced Powersupply and RS485 network
Surge
Guest
S
Hello ,
I power RS485 from an Isolated power supply which is not referenced to the Earth ground. I use the same ground return wire from each node as my supply. I want to know if the communication will run smoothly without any reference to the ground. I have no galvanic Isolation here as I think there is no need for it as I have no different ground connections I run a GND cable to each node along with the twisted pair +Rs485 ,-Rs485 .I want to ask will MAX485 work well in this application .I have a network length of approximately 100 Feet .I do someting wrong kindly letme know .
Warm Regards
RS485 should work without common ground, just by differential signal +/-. Don't forget terminator resistors!!
It will be better if you use "E" version MAX485E - it has ESD protection.
MAX485E is rated up to 2.5Mbps on much longer distances.
Depending on you application you may use MAX481E, 483E, 485E, 487E.
Just want to add:
Profibus is an example of RS485 hardware and it uses 2 -wire connection without common.
Also look at MAX3088E: it works up to 10Mb
MAX3088 pdf
Hi Contr_Conn ,
Thanks for MAX485E . I will use proper termination resistances . Please tell me is there any requirement of the third conductor wire GND along with +485, -485 twisted pair wire . I wanna know about ground to ground potential that may develop between the two nodes grounds and will this be in a safe limit if we measure it in the 100 Feet run cable . I also want to know should I tie the chassis ground and the shield ground to the circuit Electical ground as the reference from Earth Ground is missing .
I am sure, that you don't have to run a signal ground (GND) along with tisted pair differential signals.
You should terminate shield to the chassis ground on both(!) ends.
I think there is a requirement to potntial equalisation wire between devices in some cases (16 mm sq). But it shuld be run separately.
I am not sure if you have to ground a common wire (GND) of each PS to the chassis.
Look at Profibus-DP requirements, it is a true RS-485 line.
Give me your email and I will send you PDF file I have.
Please send me any info to [email protected]
You said " You should terminate shield to the chassis ground on both(!) ends "
Should I tie the Electrical ground to it .My application doesnt have a Earth Ground it is totally floating .
thanks
Why no earth ground
There is no ground connection if it doesnt do anything, EARTH is ground.
How do you ground without a ground connection..ie earth?
Personally I think its better to use either optic or galvanic isolation BUT you have to have an earth ground.
Wondering what are the pros/cons of tying Power +24VDC supply Common to chassis (earth) ground. Is it OK to do so? I have seen some control...
53
14,901
Its been a long time, I have an odd question. Is it possible for a DeviceNet network to work with no network power supply? The network scanner is...
1,894
Iam working on designing a system with Siemens S7-300 PLC.Please let me know how to decide on the powersupply required.There are 3 types of...
1,543
Hello I have a micro 1400 blown and with a solid 120vac voltage, display isn't showing up and dc output read 0v Sound like a 120v surge issue...
2,227
Hello Do i need more than 1 power supply if i have a L32E and a P4 with 7 i/o module on the same bank (connected toghether on the same line)...
1,278