URGENT HELP PLZ Mitsubishi Fx2n-8ex-es/ul
ewhite11
Jul 2007
Stockport
im not sure how to get the unit to commuicate with the PLC? can i have some ideas for logic if possible.
Cheers
You connect it to the plc block via the cable, the addressing follows on from the last octal address of the plc I/O
i.e. if the plc is a 32 I/O block then this will have Inputs X0-7 X10-17 Y0-7 & Y10-17 so if the 8 way block is the first one connected to the plc block this becomes X20-27 ( if output then Y20-27).
you don't need any logic to communicate with digital I/O cards but for analog or special function cards you use the TO & From instructions
The address of the special cards start at 0 for the first extension block.
Plug it in, it's automatically addressed to the next available addresses. There's no software or configuration required.
Hi All Dears... I Have One System With , DI : 16 Do : 16 AI : 8 AO : 8 I Am New In Automation.Also Note That I Am Using Siemens Products.Please...
2,423
hello there ppl, i have a plc-5/40 with an AB 1771-DB series B Basic module. i am using the age old PBASE software to connect to the basic...
36,291
I have an old PLC (circa 2007) consisting of Telemecanique/Modicon/Schneider Electric devices. The system has developed errors and unfortunately...
241
Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
384
I have DI module ICPCon M7024UD connect to my pc using COM3 MODBUS RTU and also RHT sensors are using MODBUS TCPIP.. The problem is, it cannot...
1,673