I'm having a bit of trouble using the 1734-ASC232 card.

I can seem to send out strings out fine, but reading strings seems to be a problem. I can send one string and it gets read into the ascii.DATA[0] array. But sending another string seems to be a problem. I have to reset the module (by going into properties of the module) to read another string.

Does anyone know how to purge the buffer of this card as it seems?

The settings I'm using are immediate read, and not master/slave, if that helps.
 
Welcome to the Forum !

One of the weaknesses of these modules is the fact that the input buffer processing cannot be triggered by a timeout or by an output command.

If you have a string that is the exact same size every time, the fixed-length function works fine.

And if your input has a delimiter character like a carriage return or line feed or escape, you can use those to trigger the processing of the input buffer. Most actual ASCII protocol strings have a delimiter.

Does your incoming string have a fixed length or a delimiter you can use ?
 
The string lengths will be of 2 different lengths, and a carriage return is used as a delimiter. can you elaborate when you say "processing of the input buffer"?

Thanks for your response.
 

Similar Topics

Hi all, I have an application coming up where I have a motor that runs forward or backward to adjust the linear position of a machine component...
Replies
6
Views
1,300
Good Afternoon , I'm using a Compactlogix 1769-L18 , with a 1734-IK , and a BEI Incremental Encoder . I'm able to get the encoder to count...
Replies
18
Views
8,937
Good Morning , I'm thinking of using a 1734-IK with a CompactLogix 1769-L18ER. Looking at the manual it looks like that it needs to be used...
Replies
2
Views
1,612
Hi everyone, As stated in the title, this is my first time configuring a 4-20mA device and I am using Rockwell's 1734-IE4C module as part of the...
Replies
20
Views
6,447
Would you fuse every module in a Point IO system or by groups? I have 3 Point IO racks and about 30 modules total of assorted IO (DI, DO, AI...
Replies
7
Views
5,987
Back
Top Bottom