Using MCA ( minimum circuit amperage) to select wire type and gauge

liberati

Member
Join Date
Sep 2013
Location
Atlanta
Posts
39
I was wondering if anyone knows how to determine MCA ( minimum circuit amperage) to so that you know what wire type and gauge to use for things e.g motors etc.

I think that if you have a panel you are supposed to take 125% of the largest motor amperage and then add that will the remaining amperage to find what the MCA is this a true statement?

Also is there a rule of thumb when finding the MCA for field devices like motors and VFD's or am I completely wrong and there is a different process to finding what type and gauge to use?
 
I think you must mean Maximum Circuit Amperage - Also called Full Load Current or Amperage.

There'd be a whole lot of troubles if you chose cable sizes based on the Minimum current.
 

Similar Topics

Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
Replies
0
Views
37
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
72
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
133
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
232
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
78
Back
Top Bottom