hello my frinds
I would like to explain to you that we have a small water treatment unit controlled by small logic controller (micro logic 1200 ) , the unit is out of order this moment due to plc (micro logic 1200 ) fault , the fault indication LED is red flashing which means application fault detected (recoverable ).
We tried to rectify the fault using RS logix 500 version 6.30.00 ,and RS linx version 2.43 .using 1747 UIC interface converter and 1761-CBL-PM02 communication cable.
The specification of the cable bulges are in page 4-16 from the user manual.
The configuration procedures we have used for RS linx are as described below .
Device name AB – DF1 -1
COM device
3 1770 –kf3/1747-ke
boad rate stat
19200 00
parity error
none CRC
stop bit protocol
1 full duplex
node 1
Name and description
status
AB-DF1-1 DH485 sta :0 COM 3 port conflict
running
By that configuration , interface ,and cable .we could not able to GO ON LINE to micro logic 1200
With the same configuration ,interface ,an other cable , using rs485 port on the UIC we can GO ON LINE for slc 500 .5/02 ,5/03,5/04
Note
- COM 3 is configured OK (control panel/system/device manager)
- The ON LED on interface is on ( USB port is powered and operational)
- The selector switch SW on the interface is on RS 232(DH485)
-The error message NO RESPOND FROM PROCESSOR ATSELECTED PATHAND NODE
- error 0x4
can you please explain to me the exact configuration of RS LINX using 1747UIC interface converter and 1761- CBL-PM02 for Micro logic 1200
-In the nanual of the ML1200 they mentioned some information abouth Default communication configuration,alsouse of the communication toggel push button
thanks
nasser al mashat
I would like to explain to you that we have a small water treatment unit controlled by small logic controller (micro logic 1200 ) , the unit is out of order this moment due to plc (micro logic 1200 ) fault , the fault indication LED is red flashing which means application fault detected (recoverable ).
We tried to rectify the fault using RS logix 500 version 6.30.00 ,and RS linx version 2.43 .using 1747 UIC interface converter and 1761-CBL-PM02 communication cable.
Ser
Catalogue
Description
Item
C
1761-CBL-PM02
Communication cable
1
A
1747-UIC
Interface converter
2
The specification of the cable bulges are in page 4-16 from the user manual.
The configuration procedures we have used for RS linx are as described below .
Available drive type
RS -232 DF1 devices
Configure RS 232 DF1 devices
Device name AB – DF1 -1
COM device
3 1770 –kf3/1747-ke
boad rate stat
19200 00
parity error
none CRC
stop bit protocol
1 full duplex
node 1
Name and description
status
AB-DF1-1 DH485 sta :0 COM 3 port conflict
running
By that configuration , interface ,and cable .we could not able to GO ON LINE to micro logic 1200
With the same configuration ,interface ,an other cable , using rs485 port on the UIC we can GO ON LINE for slc 500 .5/02 ,5/03,5/04
Note
- COM 3 is configured OK (control panel/system/device manager)
- The ON LED on interface is on ( USB port is powered and operational)
- The selector switch SW on the interface is on RS 232(DH485)
-The error message NO RESPOND FROM PROCESSOR ATSELECTED PATHAND NODE
- error 0x4
can you please explain to me the exact configuration of RS LINX using 1747UIC interface converter and 1761- CBL-PM02 for Micro logic 1200
-In the nanual of the ML1200 they mentioned some information abouth Default communication configuration,alsouse of the communication toggel push button
thanks