Using Portprint in Red lion Crimson 3
Rshepler
Jul 2014
PA
I am having trouble getting data out of a Red Lion Graphite 09. I am using the Printport command to send data to my computer. I can see the data but there is no seperation and I cannot use my software to assing it as variables. Is there a way to seperate the lines with spaces or comma's? This is all new to me and any help would be appreciated. Here is a small portion of the current version:
PortPrint(3, Main.Customer.Customer) ;
PortPrint(3, Main.Location.Location) ;
PortPrint(3, Main.Currentuser[0]) ;
PortPrint(3, Main.Names.M1_name ) ;
PortPrint(3, "M1_Flow="+DecToText(Meters.M1_flow,0,2,2,0,0) ) ;
PortPrint(3, "M1_Total="+DecToText(Meters.M1_total,0,4,1,0,0) ) ;
PortPrint(3, Main.Names.M2_name ) ;
PortPrint(3, "M2_Flow="+DecToText(Meters.M2_flow,0,2,2,0,0) ) ;
PortPrint(3, "M2_Total="+DecToText(Meters.M2_total,0,4,1,0,0) ) ;
Thanks in advance for your assistance.
Add +"\r\n" or +"\n" (depending on whether you need both carriage return and newline, or just newline on your receiving device) to your PortPrint. Or +" " for space, or +"," for comma: you get the idea...
PortPrint(3, "Hello " + variableName + "\r\n");
PortPrint(3, variableName +"',");
Portprint(3, variableName + DecToText(otherVarName) + "\n");
Do you want each item to be an individual line or one line comma separated? Either way you will probably want a carriage return at the end of your send.
Several ways you can do this. You can lump all values into a single string variable with each element separated by a comma (below).
CString SendStr;
SendStr := Main.Customer.Customer + "," + Main.Location.Location + "," + Main.Currentuser[0] + "," + Main.Names.M1_name + "," + "M1_Flow=" + "," + DecToText(Meters.M1_flow,0,2,2,0,0) + "," + "M1_Total=" + "," + DecToText(Meters.M1_total,0,4,1,0, 0) + "," + Main.Names.M2_name + "," + "M2_Flow=" + "," + DecToText(Meters.M2_flow,0,2,2,0,0) + "," + "M2_Total=" + "," + DecToText(Meters.M2_total,0,4,1,0, 0);
SendStr := SendStr + "\r\n";
PortPrint(3, SendStr);
The entire thing can be one long one but I need each item seperated by a comma or space.
Thanks Str8jCkt I will give that try.
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
38
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
83
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
138
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
260
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
79