Using RSEmulator and keep getting an error in RSLogix 5000
Forat
Aug 2015
Dubai
Hi guys, I am a total newby in PLCs, and I am currently doing a project in RSLogix 5000, using RSEmulate to Emulate the PLC, details below:
RSLogix 5000 V19.01.00 (CPR 9 SR 3)
I/O Not Responding ---> I/O OK and repeats
Under IO Configuration tree
Emualator:
Emulator RSLogix Emulate 5000 Controller Rev: 19.11
(NO FAULT)
IO module:
1756-MODULE Generic 1756 Module
(FAULT:Status: Running, Shutting Down, Offline, Faulted and repeats again.
In Connection Tab, Module Faule: Module Fault (Code 16#0203) Connection timed out.
Module Info: Module Identity Mismatched.
Backplane: a diaglog comes up saying:
"Incorrect module.
CIP object in module does not exist.
There may be a module identity mismatch or improper configuration."
RSLogix Emulate 5000 Chassis Moniter V19.01.00 (CPR 9 SR 3)
Emulator: EmuLogix5868 Controller (No errors appear on the emulator
IO Module : 1789-SIM
RSLinx Classical Professional Revision 3.51.00 CPR 9 SR 5
OS: Windows 7 Professional SP1 32 bits
I keep getting this error frequently as I open the emulator and the RSLogix program is online and it works fine, then suddenly IO not responding.
Kindly help me on this matter.
Regards,
Forat
Emualator:
(NO FAULT)
IO module:
"Incorrect module.
Regards,
Forat
All I can say is good luck!! I had to use emulate for a class I took this summer. I would spend 4 hours writing the code then 6 hours fighting emulate. All I can say is that I would shut it down, delete the simulation modules and try it again. That IO not responding was a killer though. It would work for an 1 hour then stop working all of a sudden.
I think it is crappy software.
How fast is the rpi set on your io modules? Try turning it up, from memory the default is about 10? Try 50 or so. I think this solved a similar issue for me.
That what I have been doing, it is very frustrating. RSEmulator is really bad, just a Digital IO emulator and it bearly works.
Hi Daniel, The Requested Packet Interval (RPI) is set to 50.0 ms, and still I get the mentioned fault
Why are you trying to keep the I/O module 'alive' in Emulator? Whenever I use Emulator, I inhibit all I/O modules...The tags appear and you can use all your logic, but there's no attempted backplane communication to them and therefore no errors.
I might do that, but I am keeping it alive, as to try as much as possible to recreate, an "alive plc" environment, where I get the data from the plc through the backplane of the plc, ( IO module -> Emulator -> RSLinx module ->My workstation)
But I could do that, just to check if the logic of my program.
According to RA Compatibility page, the version of RSEMulate you're using is compatible with Windows 7 Home Premium SP1 32-bit. However, there's no information about Windows 7 Pro SP1 32 bit.
Did you use the RSEMulate manual to set all the parameters in the 1756-MODULE? Did you put it on slot 3 or superior?
I think @robertmee is speaking about to inhibit "real" modules to keep their tags. You can inhibit the 1756-MODULE linked to a 1789-SIM on the emulator (or just remove it from the chassis) if you only want to test the logic.
Yeah I went to RSLogix Emualate 5000 manual page it mentions:
Windows 7 Professional (64 bits) SP1, or Windows 7 Home Premium (32 bits)
SP1, but no Windows 7 Professional (32 bits). So maybe it is the problem.
http://literature.rockwellautomation.com/idc/groups/literature/documents/gr/lgem5k-gr016_-en-p.pdf
http://www.plcdev.com/a_quick_tutorial_on_rslogix_emulator_5000
If you mean follow the steps on that page, then yes.
Well I am not working with a real module at the moment, so I am work with RSLogix Emulator, I might Inhibit the module from the Emulator Chasis as to keep the tags, without have to deal with the constant IO error.
Here's the RSLogix Emulate 5000 Getting Results Guide:
According to page 46, you need to change Input Size to 2 (1756-MODULE settings). If you followed the steps of the webpage you provided, currently you have Input Size = 1.
Try that and let us know.
No Actually I know that, There is an error in the Quick Launch Manual.
I did already put the input size to 2 (one for data and the other for fault) when I started the project.
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
28
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
64
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
125
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
225
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
61