Using S7-1215/17 to read data from two networks
leem2209
May 2015
Wirral, UK
210
Does anyone know if the following is possible?
Using an S7-1215 or S7-1217 cpu, can I read data from two different networks and then in the internal program, transfer that data (network 1 db write to network 2 db) to write to the other network?
You'd an extra CP
Dear leem2209,
The the network ports in 1215 or 1217 are in fact the same Ethernet interface with a switch. You'd need an extra CP (6GK7243-1BX30-0XE0) to connect a diferent network (with diferent IP).
Hope this helps
P1 and P2 are the same interface, which means they share an IP.
You could maybe do it with a communications card added. I think the CP1243-1 might work, depending on what type of communication you're doing.
Otherwise you could potentially use a router (S615 in a Siemens world) to act as a gateway to the other network.
Dear leem2209,
Hope this helps
Ok cool, using a CP card will allow the two different network ranges and I can have db’s reading values from each and writing to the other?
Yes, extra CP will work.
Alternatively, you could put a router between one of the built in ports and the secondary network.
Super! Thanks all...
So an extra CP card would work with a S7-1212C? We have a few spare on site.
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
36
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
71
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
132
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
229
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
77