This is maybe not the right place to ask this but since many of you have experience from VFDs I'll give it a shot.
We are some what confused regarding the functions of a new series of VFDs from our supplier. I don't want to out the company here so I'll speak in general terms.
We have used many VFDs and ofcourse it has a overcurrent protection in it. On all the other models we have used we are able to set the "motor rated current" in the parameter to a lower level then the motor actually is and the VFD will stall and after a while trip on over current.
On this new VFD we can set the "motor rated current" parameter to 0,5A and run a motor that draws 4A and it just continues to run. No stall, no trip and we have tried this well over 10 minutes. This is a 2,2kW VFD and a 2,2kW motor with no load.
We insist that this is a strange function and we don't want to start to use this new VFD if the company doesn't have an answer to why it doesn't trip. I mean, it's a very important function. We have been trying to get an answer for nearly a year now. Have anybody encountered a problem like this? Or have any ideas as to why this should be correct behaviour for a VFD?
Last I want to say, is there anyone who knows of a good place to ask these sorts of questions? Since maybe it is a bit offtopic for a PLC forum.
This is maybe not the right place to ask this but since many of you have experience from VFDs I'll give it a shot.
We are some what confused regarding the functions of a new series of VFDs from our supplier. I don't want to out the company here so I'll speak in general terms.
We have used many VFDs and ofcourse it has a overcurrent protection in it. On all the other models we have used we are able to set the "motor rated current" in the parameter to a lower level then the motor actually is and the VFD will stall and after a while trip on over current.
On this new VFD we can set the "motor rated current" parameter to 0,5A and run a motor that draws 4A and it just continues to run. No stall, no trip and we have tried this well over 10 minutes. This is a 2,2kW VFD and a 2,2kW motor with no load.
We insist that this is a strange function and we don't want to start to use this new VFD if the company doesn't have an answer to why it doesn't trip. I mean, it's a very important function. We have been trying to get an answer for nearly a year now. Have anybody encountered a problem like this? Or have any ideas as to why this should be correct behaviour for a VFD?
Last I want to say, is there anyone who knows of a good place to ask these sorts of questions? Since maybe it is a bit offtopic for a PLC forum.