I found strange situation on site, 4kW motor D400/Y660 volt wired in Y (660V) connected to 400V VFD output. Frequency setpoint was 120Hz. What could be reason for that except error?
What if that motor was wired D400 and running at 20Hz?
If you ask me, it would be OK. Motor is slower, but everything is ok and there is enough of ventilation.
I think it is important to mention that it was in closed loop (encoder feedback).
If you apply 400V to a motor connected for 660V, the motor will develop only 58% of its running torque, and more importantly, only 33% of its PEAK torque capability. Peak torque (Break Down Torque) is what the motor uses to accelerate or re-accelerate after a step-change in load. So what usually happens is that either the motor fails to accelerate in the first place and stalls, or if it does manage to accelerate because the load is very very light, it stalls whenever there is a change in the load.
It CAN however work OK if the load is roughly 1/3 to 1/2 of what the motor is capable of. Why you would have a motor that is 2X to 3X the size it needs to be is another issue though. I have run into this when someone has a motor that was designed for a different task and is being repurposed. It may be far larger than necessary but is already owned as opposed to buying a new correctly sized motor.
Thanks Jraef.
The VFD came with new motor. Application is Heavy Duty one and it needs Peak Torque. I even suggested to the client to install one size bigger motor. I think it is error, but the guy who installed it before knew how to implement closed loop vector control so I thought maybe there something I overlooked, or maybe he overlooked motor plate.
Thought about that one also, but motor is 400/660 not 230/400 and drive output is 3x400V.
Yes, you are right..
But 120Hz just sounds like alot. Especially if the setup is like Jraef says and only provides 58% torque... Raising the frequency above 50Hz (I suspect that you have 50Hz) will lower the torque, and at 120Hz it will be very low.
I might be misreading this, but the motor will develop 4kw when connected to either of those voltages, IF the wiring connections are correctly changed. If I found this situation, I'd ask around as to what the load requirements were, and probably change the motor wiring to match VFD (400V). There might be some reason why the wiring was done this way, however as mentioned above, the effective output of the motor will be greatly reduced.
A few things to think about on this
The voltages don’t sound right 400V Delta / 600V Star
The windings are usually all the same voltage meaning 400V Delta / 800V Star
The Star / Delta is usually a start up configuration to limit the starting inrush
Delta is a single winding phase to phase voltage is 400v
Star is 2 winding in series to a center point each winding is still 400v
2 400v windings in series “ Star” would be a phase to phase line voltage of 800v
You say it as a 50hz system what is the number of poles on the motor or the base speed of the motor.
A 2 pole motor at 50 hz would have a base speed of 3000 rpm
If as you say the vfd set point is 120Hz then a 2 pole motor would run at 7200 rpm. That’s way over the what would be a normal running speed and could be in a dangerous condition. Anything over 5000 rpm should be considered carefully
Most consider 3000 to 3500 rpm the max for a motor
I have done jobs where we ran a motor over 7000 rpm but I had the motor rebuilt with precession bearings and had it balanced to the expected max speed never had a problem with them but as I said before I took the time to have the motor redone to meet my needs.
Remember with an ac motor running below base speed it’s running in constant torque and variable HP and above base speed it’s running at constant hp and variable torque. With a set point of 120hz it sounds like the equipment was originally from North America with a max output freq of 120hz
400v on the vfd would mean it’s a 400v class 400v to 480v input
You can select the operating the output voltage Volts / Hertz 400v motor would be 8v per hertz that would also be the same volts / Hertz as 480v 60hz motor
What you show is possible but proceed with caution
Not in Europe
In the US there are usually motors on which the windings can be connected in pairs in parallel or in series and the voltages at which they can operate have a factor of 2 between them.
However in Europe I have never seen that type of connection and only star/delta connection with a factor of 1.73 is usually supported.
400V/690V voltages are the most common for motors in Europe, normally connected in delta, as the voltage currently used in most industrial installations is triphase 400V 50Hz
New motors usually are supplied with the links set for the highest voltage . Maybe the field guy just wired the phases the same as the old motor but didn't check the links . Duh .
Paul
I'm using an Automation Direct GS20 VFD for the first time and I have a question for the Automation Direct gurus regarding the recommendation of a...
1,103
Hello, I have an Emerson Commander SKC3400400 VFD It says Input: 3 phase Input Range VAC: 342 to 528 Volts AC My instalation is 3 phase...
2,083
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
2,627
Hello, all! Doing panel VFD (PF525) wiring. Question about the wires on the VFD T1-T2-T3 output bus. The plan is to connect the T1-T2-T3 outputs...
5,973
Hi Guys Just a quick one. I want to procure a soft starter for a Pump Motor I want to confirm this: IS SOFT STARTER SAME AS A VARIABLE FREQUENCY...
3,298