I was just presented this question do VFD's have a shelf life specifically capacitor failures prematurely. I would think this should not be an issue, but I thought I would present it to the forum and see your thoughts.

Thanks
RM
 
Yes there is. It is VERY important.
If a VFD has been out of operation for a longer time, the capacitors have to be "formed".
There must be instructions from the manufacturer as to how long shelf time requires how much forming.
 
i was told the same as Jesper and we did see some with bad capacitors...

Reforming process in general is powering them with lower voltage for a while and increase voltage in steps for hours....

Some also count shelf duration for the warranty time out...
 
We have done the same and either tap into a lower side of a transformer or applied a lower voltage to the machine, we did for all controls not just the VFD's we had one machine pulled from production and sat in the boneyard for about 2 years then brought back to life, it had a bunch of Control Techniques drives, you also need to be careful as some electronics do not like low voltage

We also had a long term shutdown and we would power up the machines once a month and run everything manually just to make sure everything would start when needed
 
Thanks guys, Jesper answered my first question and Jeff answered the second one I was about to ask. I was not familiar with Capacitor forming. Good information!
 
It takes over a year of not being powered for the capacitors to begin to de-form, but you have to go by the date they were manufactured or taken out of service, not the date they were bought. If they have been unpowered for 2 years of more, you have to use the reforming procedure, between 1 and two years it’s iffy, so just never go more than a year and you are fine.

So if you have spare drives on the shelf, one simple way to deal with this as a preventative measure it is to take them off of the shelf once per year, hook them up to rated line power on a bench (with all due safety), let them sit there like that for a couple of hours then put them back on the shelf for another year. I make up a sticker for the box that charts the PM dates.

Bonitron sells a pre-packaged capacitor reformer. It’s spendy, but it’s hard to find the parts to do it on your own too. I bought one of the Bonitron units and I made one of my own with a variac, I think I spent maybe 20% more for the Bonitron when all was said and done, but if I value my time correctly, I lost money on the DIY version, plus the Bonitron comes with a nice roller case.
I take that one around to service calls, it’s paid for itself in under a year. (No, I don’t work for Bonitron...)
http://www.bonitron.com/m3628pcf.html

If you ever buy used or surplus drives, ALWAYS do the reforming procedure, never assume the seller is telling you the thuth. A LOT of used/surplus sellers have no idea this is an issue so they just tell you what they think you want to hear.
 
Last edited:

Similar Topics

I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
78
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
184
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
173
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
310
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
13
Views
492
Back
Top Bottom