rohit_plc Member R Join Date Jun 2013 Location delhi Posts 81 Feb 3, 2016 #1 I need to invert 4-20ma ref. signal, how can we do that vfd I am using is danfoss vlt 360. Thanks
tragically1969 Member T Join Date Jun 2007 Location uk Posts 1,538 Feb 3, 2016 #2 rohit_plc said: I need to invert 4-20ma ref. signal, how can we do that vfd I am using is danfoss vlt 360. Thanks Click to expand... What do you mean by invert ?
BryanG Member B Join Date Feb 2005 Location Manchester Posts 1,990 Feb 3, 2016 #3 http://www.danfoss.com/NR/rdonlyres...tionDrive_FC360_ProgrammingGuide_MG06C102.pdf starting page 48
milmat1 Member M Join Date Aug 2005 Location North Carolina Posts 209 Feb 3, 2016 #4 Are you talking about a 4-20ma from the controller to the VFD ? The page you referenced is showing you how to scale the analog signal in reference to the Max and Min freq. I have no idea what you mean by invert an analog current signal....
redbarron55 Member R Join Date Dec 2015 Location Alabama Posts 125 Feb 3, 2016 #5 Why invert? Do you need to make the drive go the other way? If a PID then invert the PID action.
jraef Member J Join Date May 2006 Location Northern California Posts 2,141 Feb 3, 2016 #6 As the others have said, you don't invert the signal itself, you invert the ACTION taken by the drive to the signal. It's not clearly stated in that manual section, but if you understand what those parameters mean, you can do it there.