Sorry for late reply, had to go Papua New Guinea on business.
Basically the equipment is an imported Chinese spray booth which has 2 x VSD's (same models), my last visit before I went away I downloaded the program from the PLC, whilst away I analysed it and found that when changing processes from the HMI, the program would turn off the VSD's for a one program scan.
I have reprogrammed it so the VSD's stay on, this has now stopped the OVER VOLTAGE fault when changing processes.
BUT
Running both VSD's at 50 Hz for 20 minutes - no issues appeared.
I ran both VSD's at 35 Hz for 20 minutes - VSD No.1 tripped out on OVER VOLTAGE after approx 8-10 minutes even tho there was no speed change.
Both VSD's parameter wise are setup completely the same,
parameters for motor info match motor.
I've increased acc/decel times as recommend by the manual
Measured input voltage was 430V, para in VSD's max input voltage set to 440V.
I did run both VDS's with DC VOLTAGE OUTPUT displayed, VSD 1 was reading 591-598 VDC whilst VSD 2 was reading 601-605 VDC. Reading from VSD 1 was constant even to the point of tripping.
I also did swap motors going to the VSD's, and it still tripped on the VSD 1 even tho it was running a different motor.
I am completely baffled to why its trips on OVER VOLTAGE at 35 Hz, even tried at 40 Hz and still trips. With everything i have done i suspect the VSD is at fault.
With the above info can any one shed a light on the problem before i tell the customer he needs a new VSD
Thanx everyone so far for your assistance.