VSD with Fan Application
totallychibi
Oct 2005
CI
i have been asked to up-grade the current fan application with a damper to control with a VSD
im using the Fuji FRENIC FRN55P11S-4JE
so i have 415V incoming to the VSD
then this going out to the Fan Motor
there are no contactors or circuit breakers from the VSD to the motor
in the 240V control circuit,
there is a local and remote mode,
local for manual control through the vsd
and remote for control through Citect
so the PLC program,
checks that it is set to remote;
that there is no VSD fault;
and there is no isolator fault
it then enables the drive, so the operator can start from Citect and then it enables the operator to input frequencies
this only takes 2 rungs of logic
i cant think of anything else to check
the VSD will catch undercurrent, overvoltage, thermal overloads and generate the appropriate alarms
but 2 lines seems a little lacking
am i missing something very obvious?
You haven't told us much about the ductwork so I have to speculate some.
There may be intake dampers that have to open before the fan starts. You may require static pressure switches to prevent overpressurizing of your ductwork. Depending on the weather in your area, freezestats may be necessary. All of these typically form a run-permissive loop on the drive control inputs or are routed thru the controlling automation.
Otherwise, you have the basics in place.
Hi. It turns out running just inverters off of a generator is bad for the generator. Any tips? Ideally I would like to size my diesel generator...
2,463
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
210
We have an existing VSD where a three phase circuit breaker feeds the drive, and two phases also tee off to a contactor, which is energised to...
1,489
Hi all, We have an fr a740 inverter that is displaying a warning on the fr pu04 operator panel. Everything seem to be fine with the inverter but...
1,417
Hi, New to this so please bear with me. I have this controlling a Netzsch Progressive cavity pump at 30Hz and the pumps motor is rated at 21A...
3,225