i have problem with water control, let me explain the process
Customer has pump connected to vfd and controlled by plc, informations are gathered from pressure and flow transmitter. Pump has to be run at minimum of 60% (30 Hz) power because of overheating. They have water concession contract with distributer for maximum flow of 29 l/s. What they want is to maintain pressure at set value and limited flow. Water consuption varies from min to min, depends on production(its not possible to predict). I succeed to keep wanted pressure but flow is going over limit. I would like to hear your suggestions how would you stop flow from going over limit and sometimed allow to go a bit higher?
Currently Im using PID control for wanted pressure and im blocking flow by reseting PID's output, but when consumption is high, output is a bit "dancing".
Thanks forward.
i have problem with water control, let me explain the process
Customer has pump connected to vfd and controlled by plc, informations are gathered from pressure and flow transmitter. Pump has to be run at minimum of 60% (30 Hz) power because of overheating. They have water concession contract with distributer for maximum flow of 29 l/s. What they want is to maintain pressure at set value and limited flow. Water consuption varies from min to min, depends on production(its not possible to predict). I succeed to keep wanted pressure but flow is going over limit. I would like to hear your suggestions how would you stop flow from going over limit and sometimed allow to go a bit higher?