ways to backup Powerfles drive parameters
Unfortunately, the ADC (Automatic Device Configuration) feature is deployable only over EtherNet/IP on systems at Rev.20 and newer; moreover, it applies only to PF755s Rev.4.01 and newer, PF753s with 20-750-ENETR EtherNet/IP communications modules and PF525s; ADC requires Stratix 5700, 6000 or 8000 series switching for the VFD ADC subnet.
Am I correct in saying, ADC does not "require" Stratix since I can set the correct IP address in the new drive using the keypad and leave the rest to the ADC?
with drive executive, we store the parameters to the hard drive.
we then place the files on the plant network in designated folders that have a meaning to everyone.
that way, any shift electrician can replace the drive if the unit fails and they know where the parameters are.
james
So, I can use CCW to do what I can with the Executive?
You can also create .pf5 files from the offline copy of the PLC program (assuming that the parameters have been uploaded). You can then use those with a USB stick for a software free parameter download.
Yes, you should be able to trigger ADC if you enter the IP Address prior to replacement even without a managed switch.
This is only for Powerflex 525, right? Not for 70 or 700, correct?
Someone also told me not to use the HIM copycat if I can use other back up methods since the backup file stored on HIM would take up too much memory of the drive? Any thought on that?
let's say you back up all drives on your ccw - (assuming you mean display).
3 months later, it dies and you can't recover the files.
2 hours later, a drive dies.
that's why we use drive executive.
we put the files on a server that's backed up daily.
we have multiple laptops with the software, so no one laptop has the drive parameters.
james
Are you mixing up CCW with the HIM? CCW is just another software package like DriveExecutive - you can set up and save drive configurations, and then save the file anywhere you like. Unless all your copies of the file become corrupted, you're safe.
Saving a parameter set to the physical HIM - yes, that's when you've got an issue if the hardware fails.
You can use DriveExecutive for all the drives except the 520 series, but it is a paid for software that is outdated since CCW was released.
I've used Drive Executive to connect online, upload and download with 525 drives. If the AOP has been installed, or a new enough version of Logix is used that includes the AOP (you can tell if the drive shows up correctly in your Logix IO configuration), Drive Executive will work.
There is a minor hicup when connecting online. You will get two errors. One will say something about port 0, or port 1, then you get a second error. Go online again and it will connect.
I thought a free "lite" version (not including Observer) is included on the RSLogix 5000 DVD.
Thanks for the info. What is the advantage of Executive over CCW?
For me, Drive Executive seems more to the point if you just want to upload/download parameters, or go online to check parameters vs CCW. CCW you have to keep creating project files.
Drive Executive the parameter display is denser (it shows more parameters at a time), and it shows clearer what is read only, run edit, etc.
Drive Executive also has Drive Observer. Great trending tool for commissioning and troubleshooting. I believe this is the only reason Executive is still supported as there isn't a replacement for trending in CCW.
Hi All, At this time, I'm aware of at least three ways to backup a project in FactoryTalk View. Each way produces a different type of file...
11,763
hello I have 7cp476 cpu why can led always open and No connection
145
Hi all. New here and wondering if you can help. I have a flasher unit I want to test via PLC. The issue I am having is the input signal is 12v+...
204
I just graduated as a mechanical engineering student, and started this new job a controls specialist with a company in my area. My coworker has me...
977
I have a program that I am gradually piecing together (my first program). There are 4 cascading timers that turn Y001 and Y001 + Y002 on and off...
549