Dear all,
Hope that Every thing is going well with all. all I want to know is that.....
I know very well, How the block TP works..., but really I do not know what is the function of it, and what application can i use this block in.
the Block TP:
has two inputs:
1- IN >> Boolean Type : if rising edge starts increasing internal timer (if not already increasing).
- If false and only if timer is elapsed, resets the internal timer
- Any change on IN during counting Has no effect
2- PT >> Timer Type : Maximum programmed time
two outputs:
1- Q : Boolean :if true, timer is counting
2- ET: TMR :Elapsed time
any help would be great, thanks in advance.....
I know well how the block works, but for what use, and how can i use it for application?
Assuming you are talking about TWIDO, this timer is similar to the "TT" function in A/B. Use it as an interval timer. The only thing I don't like is that it can't be reset unless it times out. What is nice is you only need a momentary input to start it, so it is "self cancelling" when done, and won't start again until you want it to. You could use it to flash a lamp, run a motor for a timed period, ect, and it is externally ajustable with inexpensive keypad.
All I need in what real application
Hi tommy23t
Thanks 4 ur reply:
all I want the real application I can use this block in. TON Timer on delay can be used for what you said, what is the difference between that Block TP and Timer On Delay.
you said also it can be adjusted by keybad, How ? this block in Plc Programming, Not hardware.
Many thanks.
I am just starting to use this PLC. The diff. I see with the TON timer is you need an additional bit to use it as an interval timer and you have to keep the timer latched.
For the keypad, they have come out with the Magellis 2 line and (I think) 4 line display. You assign the timer preset to a word (like %MW150) and you access that word from the keypad. I think these keypads are under $150.00 US. They have addressable function keys if you like, but use up/down arrows to increment and decrement registers (no numeric keypad).
hope this helps,
tommy23t
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
126
Please see attached file. I need this program in Function Block form but I am totally lost on this. Any help would be appreciated. Thanks!
305
Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
542
Hi folks. New to the forum, but been working with PLCs for several years now. Would like some advice on whether you would keep this logic, or...
1,073
Hi Yes, I'm stuck again. Trying to define a Function Block. What I've put in there so far has been a straight copy/paste from the code (and that...
22
2,925