Dear all,

I need to make a control system and I don't know what PLC to use.

The system consists in:

Control of 10 digital input (0/1).
Control of 4 analogical input (measure of temperature).
Control of Inverter (frequency inverter) with communication card ProfiBus.
Remote supervision through Ethernet in a Navigator.
I need to read the variables 4 times a day in a remote place with Internet.

I use Siemens S7-200 carrying out small applications.


What PLC recommend?
How model?

Thank to all,
Mauricio
 
Hello magaete;

One of your requirements can not be met by the S7-200:
Control of Inverter (frequency inverter) with communication card ProfiBus
This can be done only through a Profibus master; the S7-200 Profibus expansion card can only work as a slave.
This would mean going to a S7-300 CPU, possibly a S7-314C-2 DP with onboard integrated digital(24 In/24 Out), analog inputs(4 voltage/current, 1 PT100) and 2 analog outputs. The -2DP extension means it has a dedicated Profibus-DP port on the CPU, so you could use that to control your drives. You would need a CP343-1 (Possibly a Lite version, if all you need it for is monitoring) for Industrial Ethernet comms. Also a S7-300 rail and Power supply. And Step 7 programming software.

On the other hand, if the inverters you want to control are from Siemens (Micromaster 420/440, MasterDrives) then these can be controlled with the USS protocol; the S7-200 can be a USS master, if you purchase an add-on library for Micro/Win (6ES7 830--2BC00--0YX0). You simply connectr to your drives with a RS-485 cable, or Profibus connectors and cable. You would of course need a CP243-1 for Ethernet comms. You could then work with a platform you already know, and use programming software you are conversant with.

Hope this helps,
Daniel Chartier.
 
Last edited:
dchartier

Thank's

I think that S7-300 is a good option. The Inverters are Danfoss VLT-5000 with ProfiBus card.

The system that you propose is:
1.- S7-314C-2 DP (PLC + I/O + Analog + ProfiBus).
2.- CP343-1 (Simatics Net).
3.- Step 7 (I have this software).

What I need to program the Web-based interface to remote monitoring? the Step 7 only?

Thank you
Mauricio
 
Hello magaete;

Look at the CP343-1IT, it has a web server integrated, might solve your problem.

Hope this helps,
Daniel Chartier
 

Similar Topics

Dear All, Currently i'm working with Endress Hauser flowmeter and AB PLC and try to integrate with 2 items. Flow meter spec using is Promass...
Replies
3
Views
35
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
Replies
2
Views
36
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
Replies
5
Views
101
Hi all smart and knowledgeable people.I have a hmi connected to 2 Plcs via ethernet.These 2 Plcs connected to control 2 systems in one machine...
Replies
2
Views
104
Dear Experts, I've come across an unusual piece of hardware for AB PLC-5 racks. I mean the NT-1776-HSD-R resolver input module. I have tried...
Replies
0
Views
58
Back
Top Bottom