Dear all,

I need to make a control system and I don't know what PLC to use.

The system consists in:

Control of 10 digital input (0/1).
Control of 4 analogical input (measure of temperature).
Control of Inverter (frequency inverter) with communication card ProfiBus.
Remote supervision through Ethernet in a Navigator.
I need to read the variables 4 times a day in a remote place with Internet.

I use Siemens S7-200 carrying out small applications.


What PLC recommend?
How model?

Thank to all,
Mauricio
 
Hello magaete;

One of your requirements can not be met by the S7-200:
Control of Inverter (frequency inverter) with communication card ProfiBus
This can be done only through a Profibus master; the S7-200 Profibus expansion card can only work as a slave.
This would mean going to a S7-300 CPU, possibly a S7-314C-2 DP with onboard integrated digital(24 In/24 Out), analog inputs(4 voltage/current, 1 PT100) and 2 analog outputs. The -2DP extension means it has a dedicated Profibus-DP port on the CPU, so you could use that to control your drives. You would need a CP343-1 (Possibly a Lite version, if all you need it for is monitoring) for Industrial Ethernet comms. Also a S7-300 rail and Power supply. And Step 7 programming software.

On the other hand, if the inverters you want to control are from Siemens (Micromaster 420/440, MasterDrives) then these can be controlled with the USS protocol; the S7-200 can be a USS master, if you purchase an add-on library for Micro/Win (6ES7 830--2BC00--0YX0). You simply connectr to your drives with a RS-485 cable, or Profibus connectors and cable. You would of course need a CP243-1 for Ethernet comms. You could then work with a platform you already know, and use programming software you are conversant with.

Hope this helps,
Daniel Chartier.
 
Last edited:
dchartier

Thank's

I think that S7-300 is a good option. The Inverters are Danfoss VLT-5000 with ProfiBus card.

The system that you propose is:
1.- S7-314C-2 DP (PLC + I/O + Analog + ProfiBus).
2.- CP343-1 (Simatics Net).
3.- Step 7 (I have this software).

What I need to program the Web-based interface to remote monitoring? the Step 7 only?

Thank you
Mauricio
 
Hello magaete;

Look at the CP343-1IT, it has a web server integrated, might solve your problem.

Hope this helps,
Daniel Chartier
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
210
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
Replies
5
Views
189
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
42
Hi All, Someone at work has put a PLC system on my desk, that's just been taken off an idle production line. He said "It's an S7 PLC. We don't...
Replies
10
Views
253
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
64
Back
Top Bottom