What Siemens PLC
saleshark
Oct 2008
nantwich
19
I hope someone can help.
I have a new project to do that requires profibus dp to four accopus drives. I am looking at using a siemens s7-300 313C-2DP cpu. Am I correct in thinking that I can configure this as the DP master and the accopus drives as the slaves?
Yes. You can do like that. For the Accopus drives there must be a socalled GSD file. This GSD file must be imported into the HW configuration in STEP7. This allows you to setup the accupus drives as DP slaves to the 313C-2DP master.
Apart from that I dont like the 313C-2DP CPU so much. Actually I dislike any "brick" type of PLC.
You get a slightly less expensive solution as compared to if you use a separate CPU and i/o modules. But any saving comes at the cost of not being able to exchange the CPU for another type if the need rises. This because the onboard i/o locks you into using that particular CPU.
Let me ask back:
How many i/o ?
Any specialty i/o ?
How complex is the program ?
Any high-speed i/o ?
Any distributed i/o besides the drives ?
Any communication requirements ?
What kind of HMI do you foresee, if any ?
Any other out-of-the-ordinary stuff that could be relevant for the choice of PLC ?
There are others on this forum that seem to "love" bricks. Strange fellers.
The programme will be pretty basic.
The application is a modular conveyor system that is already controlled by micro plcs. There is five modules on the conveyor that all require 4 outputs and 2 inputs from the main plc. I then have the four accopus drives which use Profibus and another three micro plcs that control some index units.There is also an interface with a couple of ultrasonic welders and then some positional sensors.
I hope this makes sensce, it has been a number of years since I had to build a system.
So it is "approximately"
5 x interface signals to Micro PLCs for conveyors, 4 outputs + 2 inputs each.
3 x interface signals to some Micro PLCs for "index units"
1 x interface to "welders" (how many analog or digital ?)
"some" x positional sensors (how many analog or digital ?)
4 VFD drives on Profibus.
It is not at all clear to me how many i/o we are talking about.
If this is supposed to be one integrated system, I would try to eliminate all the small micro PLCs sitting around.
And since you are going Profibus already, you should consider to place distributed i/o blocks locally where they are needed.
A 315-2DP sounds as the obvious minimal CPU choice.
You probably also must think about what HMI, and if you decide upon a locally placed panel, then you can connect it via the MPI port, leaving the DP port to handle only the DP slaves.
If on the other hand you need a HMI in a remote location, say in an office away from the control room, or you need many HMI's, then you should consider a 315-2PN/DP because of the ethernet port.
The Index units will have 6 outputs and 5 inputs.
Welders will have 3 output and 2 inputs.
The positional sensors will just be two sensors to show that parts are there to be welded.
As I have profibus, I was thinking of using a siemens ET200eco and a ET200L for distributed i/o's
The whole thing is to be integrated into one, the micro plcs are pre-programmed to run the conveyor system, so can't be taken out.
The HMI will be local.
Dont use ET200L, it is obsolete. The natural successor to ET200L is ET200S.
Integrated into one system, but still separate.
Is there a law against the micro PLCs being ripped out ?
I know what I would do.
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
168
333
153
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
912
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
122