What's 1734-ARM used for?

Mray

Member
Join Date
Mar 2018
Location
Toronto
Posts
90
Hi,


Could you please explain me what 1734-ARM (ADDRESS RESERVE MODULE) is used for exactly?
I have read the Rockwell Manual but did not get my answer.
 
It serves as a placeholder, allowing you to 'reserve' a node address for a module you don't currently have on hand.
 
Module "slot" locations in a Point I/O group are assigned in the order they are encountered from left to right. You may have a control system design that supports an option that is not always needed. This means there may be I/O modules that aren't needed and that could be left out of the system. But if you just remove them then the adapter will re-address the modules right of the opening. Enter the 1734-ARM. It is a module that simply holds a slot address for something else. The 1734-ARM and cheaper than any actual module, especially intelligent modules like analog and safety modules. So there is come cost savings to be had by using them.

Keith
 
Module "slot" locations in a Point I/O group are assigned in the order they are encountered from left to right. You may have a control system design that supports an option that is not always needed. This means there may be I/O modules that aren't needed and that could be left out of the system. But if you just remove them then the adapter will re-address the modules right of the opening. Enter the 1734-ARM. It is a module that simply holds a slot address for something else. The 1734-ARM and cheaper than any actual module, especially intelligent modules like analog and safety modules. So there is come cost savings to be had by using them.

Keith


yeah I pretty got the point but I don't understand why we can't remove the module which is no longer needed though we can add it whenever we need it at the end of the queue?
 
yeah I pretty got the point but I don't understand why we can't remove the module which is no longer needed though we can add it whenever we need it at the end of the queue?
The more popular thing to do is leave the original definition in and inhibit the module. If you physically remove it, then just change the subsequent definition module number.
 
Last edited:
If you physically remove the module, all modules past it will be detected as 1 node lower, so you have to do some extra work in your program. The 1734-ARM allows you to remove the unused module by replacing it with a cheaper module. You would also need to inhibit the module as already noted.
 
If you physically remove the module, all modules past it will be detected as 1 node lower, so you have to do some extra work in your program. The 1734-ARM allows you to remove the unused module by replacing it with a cheaper module. You would also need to inhibit the module as already noted.




Appreciate you all.
 

Similar Topics

I have a 1734-ARM card on a point IO rack. Do you need to add this card on the module list in your PLC program? Running RSlogix 20.04 and cannot...
Replies
3
Views
3,287
This is my first L1 project so I am just getting a feel for the thing. I'm thinking the ML1400 is getting long in the tooth so this is the next...
Replies
2
Views
1,578
Hi everyone, I have a AENT-R that I need to change the I/O structure around in due to customer changes in the cell. Instead of re-labeling all...
Replies
1
Views
1,856
hello,I have a project used the 1769-SDN module ,the 1769-SDN address is 0,the 1769-SDN is alarm ,the alarm code is 78 and 1 address.under the...
Replies
7
Views
2,632
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
66
Back
Top Bottom