What's the advantage of isolated DI/DO card?

RobinWang11

Member
Join Date
Jan 2009
Location
Victoria
Posts
36
Hi All,

Who can tell me what's the benifit to use isolated DI/DO module.

Our customer spec 2 modules in a project:
ALB1769IA8I
ALB1769OW81

Actually, all input/output power is from a same source, so i don't understand why they choose isolated card. Anyone can expain it to me? By the way, there is two terminals (NC) on the card. What's these terminals should connect with? Power supply? why no L and just N?
Thanks.
 
Last edited:
They are much easier to interface with a Motor Control Center because each starter usually has it's own control transformer.
Easier to mix output voltages e.g. you might have a 120AC circuit next to a 24VDC circuit.
Easier to interface with equipment that has non zero based I/O
That's to name a few reasons.
The disadvantage is you need two pins per circuit so it's harder to make High Density I/O for example 32 point
Regards
Roy
 
By the way, there is two terminals (NC) on the card. What's these terminals should connect with? Power supply? why no L and just N?
Thanks.

"NC" Stands for No Connection so there is no use or function for these terminals.

The power to run the cards comes from the backplane of the chassis.

For an input card, there will only be the signal and neutral for each terminal. The power or L signal comes from the field device.

For an output card, there will only be the signal and power for each output. The neutral gets connected at the field device.

Check out the installation manuals for the cards for examples of connections:

http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1769-in012_-en-p.pdf
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1769-in053_-en-p.pdf
 
Originally posted by RobinWang11:

Actually, all input/output power is from a same source, so i don't understand why they choose isolated card. Anyone can expain it to me?


In your specific application there may be no need for isolated I/O. However, your customer may have other machines on site that do need these modules and they are just trying to manage spare count. They may also be trying to limit any confusion from having multiple modules with apparently identical functions with significantly different wiring.

Then again, they may not understand what 'isolated' means in this context and they think they are getting something special that is really not all that special.

Keith
 
They are much easier to interface with a Motor Control Center because each starter usually has it's own control transformer.
Easier to mix output voltages e.g. you might have a 120AC circuit next to a 24VDC circuit.
Easier to interface with equipment that has non zero based I/O
That's to name a few reasons.
The disadvantage is you need two pins per circuit so it's harder to make High Density I/O for example 32 point
Regards
Roy


What are non zero based I/O?
 

Similar Topics

Ever use this instruction and what was your reason?
Replies
1
Views
891
Hi! I use a s7-1200 with a HSC single phase on input i0.0 100kHz, and input filter set to lowest 0,1uS. It is around 1300pulses on each step we...
Replies
7
Views
1,778
Hello, In our company, we are currently looking to change our way of programming since we've been growing for the last 10 year and our projects...
Replies
1
Views
5,068
Hi all, We are replacing a old SLC50/2 with a new MICROLOGIX 1220. Old inputs were wired 24vdc sinking. Is there an advantage to this? Should I...
Replies
5
Views
2,172
Dear Experts, What is the advantage if FC5 is transferred to FC6 as DATA TYPE BLOCK_FC IN Parameter? Where do I find its application? Why do we...
Replies
4
Views
4,353
Back
Top Bottom