Why did AB 1394 loose its program?
micgent
Aug 2009
Gateshead
52
I was called out to a customer, 5 axis system headed with a Bulletin 1394 5kW IMC-S series A FV3.7A controller.
Top 'Control Status' LED illuminated to indicate 'Memory fault - Setup or
program checksum error'
This occurred after a maintenance power outage!
Customer assumed it had lost its program due to a failed backup battery!
Having zero experience with 1394, PLC.net came to the rescue. Reading the threads I needed GML Commander, a 2-2 3-3 5-5 serial cable and the script file. I gained all the aforementioned, then attended site.
I gained coms and uploaded to PC (and saved) what was already in the controller and compared it to the provided script file, they were massively different. I tried the 'RESET' button and the 'RUN' function of GML Commander, which would start then end what looked to be an empty program! I downloaded the 'GOOD' script file and pressed 'RUN' things were looking up, I then pressed the 'RESET' button which I believe loaded memory into RAM working area, the machine then homed and worked.
My Question is: Does the 1394 have a backup battery? I see no mention of it in the manual. Why did the controller loose its memory?
I need to advise my customer as they are feeling vulnerable right now.
Mike
No they don't have a back-up battery.
Why they loose the program, now idea.
We have 4 systems running and in the last 12 year I've had this only one time on one of the 4 systems.
Reloaded the program, and never touched it after.
So I would say "fingers crossed"....
The RA Knowledgebase suggests that there's a lithium battery that backs up the RAM in the 1394.
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/27691/page/1
But it's not field-replaceable, so the controller would have to go through Rockwell's remanufacturing process for it to be replaced.
Hi, I have a damaged drive here in the workshop I will dismantle and inspect for lithium battery. We are an electronics 3rd party repair company so will manage battery change if we locate it.
Thank you for the advice.
micgent
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
413
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
133
In the past I have been familiar with the 1769-L35E series CompactLogix PLCs by Allen Bradley. For those PLCs (firmware version 20.19), when the...
1,169
As some of you may know I'm currently at our property in Thailand, decided to do a re-wire before taking some R&R in and around the coasts, The...
1,925
We run multiple products on our machines, which means we have multiple robot programs that we swap to, due to the points for the robots having to...
1,921