Hello everybody
Somebody know if is possible connect to Wincc with a S7-300 and SLC500/4.
Because wincc have a port MPI/DP the same that S7-300, but the SLC500 not have the same protocol..
Hi,
I have the same problem, I want to connect 2 PLC :
*S7-3005316-2DP (with free ethernet port)
*AB SLC 504
I want to connect them via WINCC, it s possible?
Thank's for the answer,
for th S7-300 i have an ethernet free port but for AB SLC504 i have an RS232 port.,i think that the DF1 is the appropriate drivers.
You welcome.
I don´t know if is possible use RS-232 direct to Wincc, I think this not possible.
But if you don´t have ethernet card for your SLC 504, so you can use OPC, with this, you will don´t have any problem.
I think that's possible with the DF1 protocol.
For the OPC solution, it's my last issue, i think to add a new module of ethernet port,have you any idea what's the model and it's possible or not?
thanks
DF1 not is supported with Wincc, this don´t work with this protocol, if you want use it, you need OPC, RSLinx Profesional or Gateway, both are OPC Server for SLC
You can change your CPU with Ethernet port to "SLC 5/05"
I have not found Communication Modules with Ethernet
take a look http://www.ab.com/en/epub/catalogs/12762/2181376/2416247/1239758/1734542/