I want to control the machine like this picture.
The machine isn't isolate the tension between Rewind and Unwind. And can change Unwind and Rewind roll, Maxspeed 250m/m
I decide to control the unwind motor with Torque mode and Rewind motor in speed mode. And I use PLC to calculate Diameter and control 2 VFD.
The Dancer is used to control the Rewind motor
Somebody have another method to control this machine.Help me plz.
Any help would be great.
Thanks ahead of time
My approach would be:
Run both in Speed Mode.
Choose one winder to be the master. It will run at whatever line speed you wish to run at.
The other winder will follow at the same speed as the master, but will trim it's speed as needed to keep the dancer in the middle position.
You will need diameter sensors or diameter calculators to know how fast to run the motor to achieve the desired material speed. To create a diameter calculator, you may need to add an encoder to one of the idler rolls so you know the actual web speed.
Do a search of this forum and you will find other applications just like yours.
Thanks kekrahulik,
I have 2 solution:
2 Drive will run in speed mode.
1 Drive run Torque and 1 Drive run Speed.
I don't know what solution is good in high speed (250m/m).
And want to Calculate Diameter what equation is good:
v=w.r
v:line speed
w:reel speed
r:radius
R = R_core + Thickness_web*N
N: round/sample_time
or you have any idea or suggest? Thanks you
http://www.plctalk.net/qanda/member.php?u=55789
I would as you said use set the unwind VFD to torque control with the speed set point set to 0 use the dancer position for torque command and set the winder BFD to speed control. but you will need some kind of speed feedback. using the PLC to set the speed will be very challenging to say the least why not use an ultrasonic measuring sensor to measure the diameter of both rolls. that way you can have the PLC slowdown and stop when the unwind roll is empty. and can have a constant web speed.
or use a tack / encoder feedback from the dancer roll speed to regulate the web speed.
keep in mind that the winder speed will start out at a high motor speed and slow down as the roll builds up. and of course the unwind motor will start out at a low speed and end up at a high speed. that is if you want to keep the line speed constant.
also to do what you want both the winder and the unwinder VFD's must have a braking resistor to dump the energy when they are in torque mode. (the energy has to go somewhere )
you may want to consider a common buss configuration
also think about how you are going to handle a broken web or an emergency stop
the unwinder has to stay on until the rolls are at zero speed otherwise on a large heavy roll it could take a long time to coast to a stop.
Hi , I Need to write a Logic for Diameter Calculation using estimated method and control of speed for Winder application . Please share if you...
2,778
Hello All, on my aplication 1-from siemen plc with aif setpoint send lenze drive with torque control value:-10% 2-send speed limitation -5%...
2,619
I've never done this before but it seems like something that will have been done a thousand times in the past. Centre winder is currently manually...
24
3,925
Hi All… I work for a company that makes bags. Operators of the machines that make the bags need to take the bags from a cardboard box that the...
1,835
Hi all, I have to program a machine with an unwinder and a winder. Currently I have 3 VFD Powerflex 527. I need your experience about this topic...
40
11,529