Hello All,
On a wire machine, i want use pid control for uncoiler and coiler with dancer.
Machine is work with error=sp-pv and main speed. When go big diameter it make oscillation. without calculate diamater how i use pid? Any advice?
Plc is siemens s7-300. Drivers are lenze.
Best regards
Nec
Originally posted bu necyil:
Generally speaking, you don't. Your PID is correcting dancer position using linear displacement at the outside of your coil generated by rotating the shaft of your coil. Since the linear displacement per degree of shaft rotation changes with coil diameter there isn't a good way to correctly apply the tangetial correction from the core if you don't know diameter. Actually, I'm not sure how you are using main machine speed without knowing diameter.
If your system is slow speed relative to the amount of dancer travel you have you could tune the system to be stable at full coil and then hope you have enough correction at core to keep up. But if you have tried that and it doesn't work you will need diameter.
There are a couple of different ways to calculate diameter that would probably be close enough for your purposes. The easiest in your case may be to add a diameter sensor. You can also use spindle speed relative to line speed or spindle displacement relative to line displacement to calculate diameter.
Keith
Hi all, I have to program a machine with an unwinder and a winder. Currently I have 3 VFD Powerflex 527. I need your experience about this topic...
40
11,455
Hello Folks, This is the design idea of a hydrogel coater that I am working on. Unwind>>Coat hydrogel>>Rewind Spces: 300mm wide web. 6000mm...
4,375
Hi, I am working on printing inspection machine where 3 nos. ACS550 of smaller rating less than 7.5Kw on unwinder, main motor and rewinder but...
2,965
Hello guys, I am trying with diferents ways for compute the actual diameter of steel strip that is unwinding and winding. I see there are many...
1,778
Hello All, on my aplication 1-from siemen plc with aif setpoint send lenze drive with torque control value:-10% 2-send speed limitation -5%...
2,605