wireless network PLC
angi
Jan 2010
us
361
Hi Guys
There are five SLC 5/04(1747-L541) on the floor, 2 of them got empty slots to use.
What I want to do is setup a wireless network which we could connect all of the 5 PLCs remotely.
What card I need to use?
Hi Angi
I havent heard about anything that fits into the slc slots, but you could use a 1761-NET-ENI ,one for each SLC and then use standard wifi components.
There is only DH+ port available for me to use on the PLC, How to handle it?
If you already have Data Highway + linking your PLC's,
Rather than buy 5 cards, just set up a Control Logixs Gateway on your existing DH+ network to ethernet and radio ethernet from that,
this option requires a 4 slot rack, a power supply, a DH+ RIO card, an ENBT or similar card all for less than the cost of 5, 1761 Net ENI's
Thats how we do it. We are linking to SLC5/04s and PLC/5s.
The rack does not need a CLX processor and you don't need any software except RSLinx to set it up. Set up takes only a few minutes. Its probably the most common (and easiest) way to bridge a DH+ network to ethernet. You can configure two different DH+ networks and bridge to both from Ethernet. From there any wireless router will do. I use a Netgear WGR16.
Unfortunately this module is for ControlLogix and not the SLC.
Clarification: Its not supposed to go in the SLC chassis, its supposed to go in the 4 slot 1756 bridge chassis that Gil mentioned. If you choose to use the Prosoft MVI56-WA-EIP module I believe you can skip the 1756 ENBT since the MVI56-WA-EIP has bridging capability, you should only need this plus the 1756 DHRIO card, 4 slot chassis, and power supply - but its best to talk with a Prosoft tech to make sure.
BTW, anything that you put in a SLC chassis is not going to be able to access the controller program/memory over the chassis backplane, the SLC backplane will not support that kind of communication. Pass thru requires a jumper between the module and the processor's programming port. Not a big deal, you just need to be aware of the limitation.
Thanks guys
Any body knows how much it will cost for 4 slot rack, a power supply, a DH+ RIO card, an ENBT or similar card ?
Thanks again
Looking for some help. I posted this on the Ubiquiti forum: Just joined the community, please be patient with me as I have, being kind with...
28
6,515
Hi I had previously bought a cheap router ($50) so I can setup a wireless network in the plant. The plant had say 4 PLCs and 4 SCADA clients...
4,116
Can it be done ? I've seen suggestions with routers etc. but surely this would be if I wanted to create my own wireless network ? How do I go...
7,612
I was given this task to connect out PLCs to the network wirelessly so they can use the data that is on the machines. I have ben given the...
17
4,196
I have a very simple wired network using a L32E processor, panelview plus, HP switch and my laptop. I would like advice on what hardware is needed...
2,433