Wonderware with Siemens S7-300 (DASSIDirec) Problem
marwan_13
Sep 2006
Amman-Jordan
28
Hi all Siemens Expert..!
I’m currently working on an interface communication with a Siemens S7-313, connected via Ethernet.
Here is a list of the configuration made in the project:
PLC:
S7-313-2DP
CP Card 343-1EX11-0XE0 (IP: 192.168.0.2 subnet 255.255.255.0)
Server:
WinXP Server 64 Bit , firewall off.
IP : 192.168.0.98, subnet 255.255.255.0
Network card is setup accordingly.
I’m able to ping the PLC, all 4 32 bytes packets coming back under 1ms.
Archestra:
SMC Version
DASSIDirect2
Under that branch, I have a node called S7300, with the port type “S7Cp”
The parameters at this node are the following:
-Processor type : S7 PLC
-IP: 192.168.0.2(The address of the S7 controller)
-Local TSAP : 1.0
-Remote TSAP : Rack No.: 0 -- Remote Slot No.: 3 -- Connection Resource : 3
-PLC Connectivity activated, frequency equals to 60 sec.
-Reply timeout : 15000ms
-connection timeout: 30000ms
-Alarms & events disabled.
Now for the device group:
-Name is “Master_PLC”
-Poke mode : Full optimization
Wonderware:
InTouch Window Maker Version 10.5
-Access name : Master_PLC
-Access : Master_PLC
-Node name : none
-Application Name : DASSIDirect
-Topic name : Master_PLC
-Protocal : Suite Link
-Advise only active items
-Secondary source disabled
Shall I need to configure CP card communication in siemens to work?
Regards,
Marwan
You should have just configured the CP itself. You dont need to configure the Server.
However your remote slot should be that of the CPU slot 2.
In your Wonderware configuration if your DA server is running on the same machine either put the machine name,IP, or localhost or localhost IP. But you have to reference on which node the DAS is.
Ok many Thanks.. Regardsing CP card .. when I open diagonstic it's Run but Send/Receive not configured... do you how to configure?
Regards,
Marwan
You should not have to configure send receive for communication with intouch. That is for inter plc communications between CPUs.
After you change your Nodename post Pictures of condig. Also post your SMC log file for extended diagnostics
hi. On my SMC, under DA server manager, I can only see FSGateway, can't see DASSIDirect2, or any other OEM.
What do I do
You have to install the driver you need from the Intouch device drivers installation medium. Or if you are registered at AVEVA, you may be able to download it from there. Since it's AVEVA it's complicated where and when you can download something.
Hi all, Got a client who has requested a SCADA system for downtime tracking and so on. Right now, they want to implement it as a standalone...
20
7,932
Hello, I need to be able to write time directly to a Siemens TON SFB4 timer. How can I do that through Wonderware Intouch using DasSiDirect...
4,774
Good morning guys. I'm posting here because I have a situation that I can't solve.. we are migrating from intouch 10.1 to 17.2 and we install...
1,667
Hi, I would like to ask, does anyone of us have experience in communicating by ethernet between Simotion D435 and Wonderware InTouch? Is it even...
1,368
Hello Everyone, I use PLC S7-400 with Ethernet module CP 443-1 and i want to communicate with My galaxy via DAServer. I configure my PLC with...
3,451
