Hi All,
I am working on a project using Woodward Easygen 3200 and a PLC for remote control. I have figured out how to run the generator remotely as well as control the circuit breaker using the Logics Manager and internal inputs. However, it was stated in the configuration manual that the remote start can only be done while in Auto operation mode and the breaker closing and opening can be done remotely with the controller in Manual mode. Is there any way we can control both only in one mode? I am thinking of switching the modes auto and manual using discrete inputs but I also would like to ask you guys if there are other ways.
Thanks in advance.
I am working on a project using Woodward Easygen 3200 and a PLC for remote control. I have figured out how to run the generator remotely as well as control the circuit breaker using the Logics Manager and internal inputs. However, it was stated in the configuration manual that the remote start can only be done while in Auto operation mode and the breaker closing and opening can be done remotely with the controller in Manual mode. Is there any way we can control both only in one mode? I am thinking of switching the modes auto and manual using discrete inputs but I also would like to ask you guys if there are other ways.