Worst thing to ever happen!!
Reading these recent ones reminds me of similar ones...
Working at my first commissioning job in a new factory, I was learning off the electrical contractor's technician. Dealing with Starkstrom VFDs, and yes he was measuring 4-20mA initially then went to measure the output voltage, and BANG went the Fluke meter. Thankfully I was standing a bit away from him, but he was not injured. Lesson learned - check the leads....
Same factory, few years later, once I had my feet under the table. I had been on call only a few times, and asked to come out to have a look see, as some analog values were not reading correctly from a PLC5 1771 remote rack. Out I came at 1 in the morning, discussed the issue with the shift tech, then got my meter etc and a torch. Up to the panel, looked at 16 slots of 1771-IFE analog cards - they all appeared to be indicating correctly, but readings were not right on any the channels. Looked around the panel, saw an open-case 24V DC power supply, went to measure it, and it seemed OK at 24V DC, but was not steady. So, isolate and disconnect to check on no-load. Isolated, then went to remove wires. Got a flash and a belt off the output wiring as I was trying to remove it. Better check the isolation again. Yes it was off, so no 24V DC. changed my meter to AC, measured a not steady 400V AC on the DC output.
Cannae remember all the detail, as I was still a bit dazed from the 400V belt I had got. The shift tech was concerned for me too...he still thinks he tried to kill me that night.
Upshot was that a Danfoss Oil Filled VFD had been replaced that dayshift, and it had a faulty 4-20mA card, such that the rectified voltage had somehow found its way back through the analogue lines and not blown the 24V Dc power supply, but had fried all the Analog Input cards on the rack.
We did not have enough spares, neither did Allen Bradley, so took a couple of days to get the parts shipped to us and get the line back up and running.
Thankfully we started phasing out the Danfoss Oil-Filled VFDs after that...
A funny one that I can recall off the top of my head was when I was an intern.
The engineer I worked under left early for the day to enjoy a mountain bike ride. He asked if I was good with staying behind for the rest of the day. Having been there for a few weeks I was starting to feel confident so I said "sure enjoy your ride".
A few hours later one of our main assembly line went down. While trouble shooting the logic, I thought I found the sensor causing the issue. However, not mater what I tried, I could not get it to change state.
Finally succumbing to defeat, I called the engineer and to my surprise, he answered. He raced back to the trail head so he could use his cell phone as a hotspot and remote in to help me out. As soon as he logged in he sighed heavily and said..."you know you are not online with the processor right..." Luckily he was really cool about it...he only ragged me a bit. And he said he broke his personal best time going down the trail that day...so I guess in a round about way he owes me ;) lol
Ran a firmware update on a datalogger and this is the horrific splash screen it showed when the update is running. Genuinely thought I'd bricked...
1,287
Posted just because it's has an Allen Bradley keyed selector switch https://www.youtube.com/watch?v=YeFevEGoPF0 LockPickingLawyer
2,729
Can anyone show any worse example for this indescribably tacky marketing approach for industrial components? Control Techniques make GREAT drives...
3,784
For years I believed that Siemens Simatic Basic panels where the worst panels ever with no reason to exist. That was until I was forced to work...
3,155
Hey folks; I have been a long time lurker and an occassional poster and was curious if you think that PLC.net has got to be the best or worst...
17
9,781