In Flex sp2 in faceplate editor, I want to make a button visible when a external tag from plc (mw100) has value 4.
In the designer, I can only create a internal tag because I cannot acces the dynamic property: visible
Now I have to do something with that internal tag like internal tag := mw100.
How can I do this?
Select external tag > Events > Change value > Set value > Tag (Out) = internal tag, Value = external tag.
Should work, the other way around doesn't for some reason.
Nice tip...
It seems I cannot address this internal tag. In the faceplate editor, the tag is listed under:
ScreenModuleProject->Device->Communication->Tag
Do I have to write a script or something?
script would work too but the suggestion above should have sorted you out.
What data type is your internal configured as?
Well just found it,
I use a switch button.
The visibility variable is labelled under: Switch->Image->Graphic on and Graphic off.
Annoying that the name is suddenly different from normal use.
Also I don't know what ScreenModuleProject is...Maybe some sort of VBA submodule.
I couldnt see the tag in Wincc connections
Any chance you can elaborate on the external to internal tag link?
My external tag cannot see any internal face plate tag when I try a "set value" system function within the change value event of an external tag.
-Cheers
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
34
Hi everyone, I hope you're all doing well. I'm currently working on updating an HMI project for the GP2500, and I've encountered a bit of a...
102
I've gotten to the learning curve where I can program a call for pump to come on at set point but I'm not sure how to turn the same pump off when...
141
Hi everyone, I am working on a project that needs to expose the SV (Set Value) of a temperature controller to a SCADA system. SCADA <-...
167
Thank you for any and all responses/help. I have an RSLogix 5000 v20 and a Cognex In-Sight v5.9 spreadsheet (8502P). I can not figure out how to...
138