RSStudio 5000 error,

Attempted to import a module L5X to a project. The previous module occupying that Module name and IP Address has been deleted.

Where would this error be coming from?


Importing...
Creating module: 'IO_C7715'
Error: Unable to import "IO_C7715". Failed to set the 'Address' property (Attempt to set an address for a port that doesn't occupy an address.).
Import failed - 1 error(s), 0 warning(s) - No changes were made to the project
 
That's a weird one !

Did you delete the Module-Created Tags and associated Module-Created Data Type also from the project ?

What kind of module is it that you're importing ?
 
Figured it out...

I can delete the cards, but I have to leave the root device there for the import to work. It was trying to set and address for something that didn't exist. Why this limitation exists I don't know, the module details exist in the L5X so it should be able to add the whole package.
 
ALso only the 1794's seemed to be affected. 1734's were happy to let us clear out the module and import it as you'd expect you should be able to.
 

Similar Topics

Hi Everyone I am currently using an SLC0505 and Logix500 as house-control at my home. I want to upgrade to ControlLogix and Studio5000. Does...
18
Replies
3,494
Views
How can I import my tags in 5000 into Studio? I see how to export them to a CSV, but studio wont read a CSV....help please???
5
Replies
3,939
Views
I'm working on getting some alarms on a panelview plus 1000 on our production line from a plc controlling the hydraulic pumps for this line. All...
2
Replies
1,701
Views
About 2 years ago, I upgraded 6 workstations to Rockwell Rev 26.0. This included all the RsLinx, and RsNetworx, and rsView revisions that were...
3
Replies
2,093
Views
Hello all, I'm having a problem connecting to a L71 that has v20 of rslogix. The plc is not being found with RsLinx but I am able to find it...
0
Replies
11
Views
Top