tadams73 Member T Join Date Nov 2008 Location Tennessee Posts 25 Jan 15, 2010 #1 What is the max length of a RIO network on a 1746-SN.
sthompson Lifetime Supporting Member + Moderator Join Date Jan 2007 Location Vernon, BC Posts 1,852 Jan 15, 2010 #2 tadams73 said: What is the max length of a RIO network on a 1746-SN. Click to expand... I presume you mean a 1747-SN. The Maximum Length depends on the the Baud Rate. Where 57.6 kB is the most common. Installation Manual - Have a look at Page 10; http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1747-in060_-en-p.pdf User Manual; http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um013_-en-p.pdf Stu.....
tadams73 said: What is the max length of a RIO network on a 1746-SN. Click to expand... I presume you mean a 1747-SN. The Maximum Length depends on the the Baud Rate. Where 57.6 kB is the most common. Installation Manual - Have a look at Page 10; http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1747-in060_-en-p.pdf User Manual; http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um013_-en-p.pdf Stu.....