OkiePC
Lifetime Supporting Member
I think you guys should post some electrical drawings to clarify what you are explaining.
No, the two channels would be used exactly like you would an E-stop with two contacts. So, 13 & 14 of the first relay in series with 13 & 14 of the second relay then feeding into one channel of the master, while 23 & 24 of the first relay are in series with 23 & 24 of the second and feeding into the second channel of the master.when you say put the outputs from the safety relays in series do you mean 13 & 14 and 23 & 24 in series then take them to one I/P to the master and then the same on the other safety relay and feed them outputs to the second channel on the master?
I agree completely. This is a poor practice at best, and simply unsafe if they have chosen to not use safety rated devices, too. I believe door contacts and E-stops should be monitored directly.to me this [door contacts and e/stops feeding small relays that all the N/O contacts are in series and feed the safety relay] isnt such a good idea apart from been easy to see which one is at fault, what do you think??
When I wrote about "two MGR's" from one device, these are connected to the outputs of the Master. These two are where you make and break the E-Stop Controlled Power to the rest of the machine. From the PLC, there is only one MGR. Two NO contacts from this one relay are used, once again the same way you would an E-stop PB with two contact blocks, in the circuit that feeds the Master. When finished, terminals 13 & 14 will have three devices wired in series between them; the first channel output of the E-stop PB safety relay, the first channel output of the Gate Switch safety relay, and one contact of the MGR from the PLC. Terminals 23 & 24 will be wired similarly with the second channel outputs and the other MGR contact.the two mechanically guided relay contacts do you mean wire each of the two MGR in series with the E/Stops input to the safety relay and the other MGR in series with the Door safeties or would you wire them to the terminal outputs from the slave safety relays that feed the master safety relay?
sorry i do have another question while we are on the subject, when i was at Allen bradley we did go through the use of MCR in the program but they don't go through the use of them in a factory or how you stand from a safety point of view, would you use them in the program to isolate outputs or would you not go to the trouble as i have heard they can be a pain in fault finding.
Rob