i am working with a project in which i want to communicate my PLC(ML-1400 SERIES-A) with popular micro-controller called ARDUINO using modbus protocol
so my idea is i have made arduino as a modbus master and PLC(ML-1400 SERIES-A) as modbus slavei have downloaded the modbus master library for arduino
now my question is whether i need to do any sepreate programming for PLC to work as a modbus slave or only my simple programm which i have written for tank level control is sufficient??
i have also attach the screen shot of my channel configuration
is this sufficient or i need to do separate programming for configuring my PLC as modbus slave
waiting for the reply
Whether I need to do any seperate programming for PLC to work as a modbus slave, or only my simple program, which i have written for tank level control. is sufficient??
I don't see your simple program, but it must have special characteristics using Message (MSG) Instructions, as shown in the MicroLogix 1400 Programming Reference Manual, Appendix D, Protocol Configuration, Modbus RTU Protocol, Modbus RTU Slave, starting at page 580, and also in Chapter 22 Communications Instructions.
Message instructions are used to transfer information between the data files in the Modbus RTU Master and the Modbus RTU Slaves. Refer to Chapter 22 for detailed information about configuring a MSG instruction for Modbus Communications...
The Modbus RTU Slave driver maps the four Modbus data types—coils, contacts, input registers, and holding registers— into four binary and/or integer data table files created by the user....
The coil and contact files can contain up to 4096 coils or contacts in each register when the data table file is configured for a maximum size of 256 words. Each input register and holding register file can contain up to 256 registers when the data table file is configured for a maximum size of 256 words. With the “Expanded” box checked, the controllers can be specifically configured to use up to six 256-word data table files for a total of 1536 Modbus Holding registers.
I have also attached the screen shot of my channel configuration. Is this sufficient, or do I need to do separate programming for configuring my PLC as modbus slave?
Comparing it with the example in the manual, it appears to be sufficient.
Thank you so much sir for your reply
i have read the manual but on page number 354 its written that it can be used only with the modbus master
also on page number 388 they have given the example but it is for modbus master
i am confused please tell me whether i can use MSG instruction as a modbus slave or not
thank you so much for your time
waiting for your reply
As a Modbus Slave the PLC does not initiate any messages (MSG instruction). As a Modbus Slave the operating system reacts automatically to external requests from a Modbus master providing the contents of (and accepting new values for) the registers which have been designated in the Modbus configuration. This is done automatically without any ladder messages needed.
thanks sir for your reply
so it means that i need not to do any special ladder programming as i have selected PLC as modbus slave
so now i can start programming in arduino to communicate with my PLC
thank you so much
i will be back if i have any doubts
The "special programming" will need to be done in your Ardunio, where you tell it exactly where all the addresses are in your MicroLogix 1400. In other words, your Ardunio Modbus Master has to both write to addressses in the ML, and read data from the ML, in order for it to communicate.
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
52
108
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
229
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
311
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
669