E stops
ganutenator
May 2002
kansas
1,440
We use a force guided idec relay for our e stop circuit.
Having problems recently getting the product.
Are force guided relays really necessary?
I've never seen a mA ckt weld contacts.
I am sure you can get a force guided relay from another manufacturer as a substitute? You would need to replace with the same type to maintain the machine's safety function. So yes, you would need to replace with a force guided relay.
Allen Bradley 700-HPS2Z24 if that's something like you use? My supplier has 100+ in stock
/Tim
If you use only 1 channel of the relay, it doesn't matter. PG relays mean the n/o and n/c can't be true at the same time.
If you're only using say the n/o, it makes no odds.
For E-stops, which this thread is about, the minimum PLr is "c", so that means you need multiple contacts for either switching through the activation and/or for the diagnostics channel.
I am also certain that "force guided" means that there is less probability of a contact sticking, so even for a single channel with no feedback it will be safer.
edit: Thinking about it, in that case it is the ONLY safety !
And, the codes require force guided contacts, why are we even discussing this ??
Sidenote. If you have trouble sourcing relays with force guided contacts, then use a plain simple contactor instead. These (almost) always have force guided contacts.
I have only experienced an AB contactor where it says in the specs that its contacts are not force guided. Any other contactor also mini-contactors I have ever encountered have force guided contacts. And you usually get huge discounts on standard devices such as contactors so it is not more expensive.
So, we only use contactors in safety circuits.
Hey guys. currently running an automation system that includes 60 Panasonic servo drives with STO function. Omron PLC tied into the safety system...
22
1,070
Hello, I have a compact Logix plc and I have been task with configuring alarms into our SCADA when an Analog signal stops moving. The analog...
240
Have a customer that has a running 1756-l83es, communicating to redundant ABCIP IO servers for Wonderware 2020. This configuration has been...
876
Hi. I'm trying to update the firmware on some ControlLogix's. They're being polled by an IGS driver. After the upgrade, my floats and integers...
1,384
Hi all. This is my first time working with the CCW software, and I'm using the CCW developer edition version 21. The PLC is a Micro870...
1,503