OTE instructions not sending signal to corresponding outputs
Memory
Aug 2021
NC
When I force the outputs, some of the LED’s on the card to not correspond to the tag. Pt00 through Pt03 send a signal to the correct outputs.
Pt04, Pt05, and Pt06 send signals to 9, 10, and 11 respectively, on a 5069-OB08 output card.
What would cause this?!?
Program tag Corresponding LED (slot 5)
Local:5:O.Pt00.Data 0
Local:5:O.Pt01.Data 1
Local:5:O.Pt02.Data 2
Local:5:O.Pt03.Data 3
Local:5:O.Pt04.Data 9
Local:5:O.Pt05.Data 10
Local:5:O.Pt06.Data 11
Forcing an output with Allen-Bradley systems does not mean you are forcing the output tag. In fact, you are overriding the logic and forcing the PHYSICAL output to energize or de-energize. The output in the logic (and the tag) is unaffected. So, it is entirely common where the output tag will have a zero and show de-energized, but the physical output has turned on. The red "ON" indicator below the instruction is your indication that the field device is being forced on.
Forcing an output is like placing a jumper wire with 24V on the output point. The output will respond, but the logic has no idea you have done that.
OG
Right, but it's the physical output that isn't responding.
When I force Pt01, physical output one turns on.
But when I force Pt04, physical output nine turns on.
When I force Pt05, physical output ten turns on.
When I force Pt06, physical output eleven turns on.
I started running the forces because the output devices (in this case valves) were not being actuated with the program logic was showing the OTE's were going true.
Pt01 through Pt06 go to the same types of valves.
Pt 01-Pt03 send a signal to their correct corresponding outputs.
Pt04-Pt06 are sending a signal to the incorrect PHYSICAL output.
I am at total loss.
Yeah, and I didn't word my response very well. I went back and edited it.
That got me too. It was like wait, it is only an 8-pt card, how would it have indicators above 7? Didn't make sense until I saw the diagram.
OG
Pt4(output 4) is pin(terminal) 9.
Check your coil wire to make sure it is not connected to pin(terminal) 4. That is the common for the first 4 outputs
For this reason I HATE Rockwell/AB cards... Lets start the IO in logic at 0.. on the terminal strip at 1.. count commons as part of the normal terminal number... etc. a 16 point card ends up with 39 terminals... what a pain in the *** to explain to techs remotely. I've started writing the terminal numbers into the IO sheets I generate for facility MCCs.
S5, S7, B&R, Baumuller. I have it like that on them all. I agree. I like to see DO5.4 pin 9. A new piece of hardware can drive me crazy. I believe it is a manufacturing point because the same case is used for 8 pt, 16 pt, isolated outputs, and on and on.
Can I use multiple OTE instrutions for the same tag at various different routines inside the program? I know that doing this would cause issues in...
7,655
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
196
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
284
Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
89
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
220