I saw another thread similar to my issue but I have different equipment and didn't want to jump on that one so here is mine:
PanelView 600 2711-B6C2 Rev. C Frn. 3.30
SLC 5/05 1747-L551 Ser. B Rev. 4
1761-NET-AIC Ser. B
Windows 7 Pro 32 bit
RSLinx Classic Pro 2.59.02 CPR 9 SR 5
My PC is connected to the AIC module using 1761-CBL-AP00 Ser C
The PV 550 is connected to the AIC using 1761-CBL-AS03 Ser A
And the SLC 5/05 is connected to the AIC using 1747-CP3
External power switch is on with 24VDC external applied to AIC and Auto for baud (tried 19200 as well)
Node address/Baud setting in PV is Node 2, 19200.
In RSLinx I selected RS-232 DF1 devices, Auto configure. SLCCH0/Micro/PanelView is configured and communication works with the processor through the AIC.
Browsing in RSLinx, Node 0(PC) and Node 1(SLC) are found but not the PV. Under Config-Communication in the PV the comm led is flashing and "No active nodes found on network" is displayed.
Now I read somewhere that you have to configure channel 0 in the SLC to DH 485 so I tried that. I lost all communications with the processor completely after I downloaded the change and had to reset it to factory defaults and re-download my program(not a big deal, small ladder and PLC is for testing only). I know I'm missing something here but I just can't see what to do next and would greatly appreciate any assistance.
The ultimate goal is to get communication established over DH 485 in order to work on a PanelView 550 2711-T5A2L1 Ser. A Rev. E Frn. 4.10 which is not functioning properly and I want to see if I can at least get comm's established to possibly download a new PVA application and bypass/remove the current program/password. Since I am unable to get to the config. screen I am using the PV 600 in lieu.
PanelView 600 2711-B6C2 Rev. C Frn. 3.30
SLC 5/05 1747-L551 Ser. B Rev. 4
1761-NET-AIC Ser. B
Windows 7 Pro 32 bit
RSLinx Classic Pro 2.59.02 CPR 9 SR 5
My PC is connected to the AIC module using 1761-CBL-AP00 Ser C
The PV 550 is connected to the AIC using 1761-CBL-AS03 Ser A
And the SLC 5/05 is connected to the AIC using 1747-CP3
External power switch is on with 24VDC external applied to AIC and Auto for baud (tried 19200 as well)
Node address/Baud setting in PV is Node 2, 19200.
In RSLinx I selected RS-232 DF1 devices, Auto configure. SLCCH0/Micro/PanelView is configured and communication works with the processor through the AIC.
Browsing in RSLinx, Node 0(PC) and Node 1(SLC) are found but not the PV. Under Config-Communication in the PV the comm led is flashing and "No active nodes found on network" is displayed.
Now I read somewhere that you have to configure channel 0 in the SLC to DH 485 so I tried that. I lost all communications with the processor completely after I downloaded the change and had to reset it to factory defaults and re-download my program(not a big deal, small ladder and PLC is for testing only). I know I'm missing something here but I just can't see what to do next and would greatly appreciate any assistance.
The ultimate goal is to get communication established over DH 485 in order to work on a PanelView 550 2711-T5A2L1 Ser. A Rev. E Frn. 4.10 which is not functioning properly and I want to see if I can at least get comm's established to possibly download a new PVA application and bypass/remove the current program/password. Since I am unable to get to the config. screen I am using the PV 600 in lieu.