Old March 24th, 2021, 06:04 PM   #1
JPLYNCH
Member
Ireland

JPLYNCH is offline
 
Join Date: Jul 2017
Location: Dublin
Posts: 13
Mitsubishi HMI com cable wiring

Hi guys

I am having issue with com error popping up on a GT2104 when I press the HMI screen. I set up a full program and thought i had a problem with that so i basically set up a simple bit button on it and sent it to the HMI so just a simple on but i keep getting com error. The cable is brand new from trusted supplier. This is my first time programming HMI and PLC in lonnnnng time so maybe I am doing something really silly or not? Attached are photos of hardware and connections. Maybe it is my wiring? Any help to an old newbie would be appreciated
Attached Images
File Type: jpg 20210324_134808.jpg (176.1 KB, 11 views)
File Type: jpg 20210324_143741.jpg (141.1 KB, 9 views)
File Type: jpg 20210324_143738.jpg (149.8 KB, 9 views)
  Reply With Quote
Old March 24th, 2021, 06:59 PM   #2
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 605
I am not familiar with the Graphic operator Terminal from Mitsubishi. But the terminal shows RS845 label and I do know that the RS485 specification calls for terminator resistor. Also, if this Mitsubishi does not support baud rate auto detection, then you have to match the baud rate settings from the GOT touch panel or the GOT programming software and on the PLC program. Hope this helps.
  Reply With Quote
Old March 24th, 2021, 07:43 PM   #3
goghie
Supporting Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 421
What is the PLC model?
Judging by the cable it should be FX3G, FX3S, FX3U, FX2N or FX0S.
Also if it is original cable on other end there is MiniDIN connector.
Also in that case RSA and RSB should be connected as well.
  Reply With Quote
Old March 24th, 2021, 07:50 PM   #4
JPLYNCH
Member
Ireland

JPLYNCH is offline
 
Join Date: Jul 2017
Location: Dublin
Posts: 13
It is an fx3s se image attached
Attached Images
File Type: jpg 20210324_130910.jpg (192.5 KB, 16 views)
  Reply With Quote
Old March 24th, 2021, 08:42 PM   #5
goghie
Supporting Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 421
Find attached example and pinout.
HMI example application reads D8001 system register.
Also to note, that you have ordered GT01 cable with DSUB connector on the other end and removed it, so I'm not sure if colors are identical.
You should order GT10 cable and use this pinout.
However it will work if you connect both sides according to diagram.
Attached Files
File Type: zip got_fx3s.zip (36.2 KB, 5 views)
  Reply With Quote
Old March 24th, 2021, 08:51 PM   #6
goghie
Supporting Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 421
Also according to your picture you have connected CSA and CSB instead of RSA and RSB.
CSA and CSB is for 5V supply from PLC.
RSA and RSB is for RS422.
  Reply With Quote
Old March 25th, 2021, 04:18 AM   #7
JPLYNCH
Member
Ireland

JPLYNCH is offline
 
Join Date: Jul 2017
Location: Dublin
Posts: 13
I tried the connections as you sent in the diagram and still error. I asked the supplier when he sent the plc and hmi to provide me with the cable between the 2 and that one was what he sent so i assumed it was the correct one. Obviously it is not and I will have to get the right one as i cannot get this one to work
  Reply With Quote
Old March 25th, 2021, 04:31 AM   #8
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 3,149
Try putting the Baud rate to 9600, Mitsubishi FX default to this after boot, although for GXDev/Works it auto tests & will set the PLC to the correct baud rate as did the Beijers (Mitsubishi badged HMI), however, I'm not sure about the GOT's, It's worth a try, however, I would expect they should.
As far as I know it is not possible to set the programming port parameters, at least I have never seen any info on this whereas, the addon ports are configurable.
I came across this some years ago, I connected a Scada system using Kepserver & ethernet to 422 converter, It worked fine after installing but after a machine shutdown, it stopped communicating, changed the baud rate to 9600 & it worked fine, I found out later that if I set the converter to 115000 then go on-line with the SC09 cable at 115 kb then plugged in the scada it worked, spoke to Kepserver & they confirmed that the PLC will default to 9600 & they were looking into auto config of the PLC.
  Reply With Quote
Old March 25th, 2021, 04:39 AM   #9
goghie
Supporting Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 421
From my experience Gt2104 works flawlessly with FX3S as with any other Mitsubishi PLC. I suggest that you don't look at colors of wires in cable but pins, because it is not GT10 but GT01 cable.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Communication between keyence HMI and Mitsubishi PLC Ltpriyank LIVE PLC Questions And Answers 9 February 15th, 2021 09:48 PM
Mitsubishi FX2N PLC & HMI communication e_pramod LIVE PLC Questions And Answers 17 November 1st, 2016 01:47 PM
pls help me about Proface HMI GP470 cable somnamon LIVE PLC Questions And Answers 0 August 9th, 2012 11:08 AM
Programming a Mitsubishi HMI DKarasin@gmail.com LIVE PLC Questions And Answers 3 July 11th, 2012 06:29 PM
PC communication with Mitsubishi HMI Lou LIVE PLC Questions And Answers 5 October 12th, 2006 12:49 AM


All times are GMT -4. The time now is 08:35 PM.


.